Axiom Puropal water conditioners for steam

Mark Eatherton
Mark Eatherton Member Posts: 5,858
Greetings fellow Wallies. Has anyone here ever had any experiences with the Axiom Puropal water conditioners for use in steam heating applications? Positive or negative, looking for all feedback.

We have tested the water before and after and are impressed with the results, but did experience some water line bouncing (steam) after we installed the cartridge. I suspect dirt from distribution worked its way back top the vessel, bit wanted to see if anyone else has had the same experience.

Thanks for your input.

Mark Eatherton
Service Director
Advanced Hydronics, Inc.
Denver, CO

There was an error rendering this rich post.

Comments

  • hot_rod
    hot_rod Member Posts: 23,218
    check th ph after a few days, the cartridge could pull it down into the high 6. Steamers like to run a bit alkaline
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    Thanks for the advice HR. It's only on the make up, so it only conditions upon draw, but will take you advice to heart.

    Much appreciated.

    ME