Baxi 380 heat exchanger leaks
ccaissie
Member Posts: 1
I have replaced the o-ring/gaskets on this unit several times. I do not know how this fails, but periodically there must be a pressure spike and it blows out the rubber donut, causing a mis-fit against the exchanger surface. Each time, I find one of the donuts has been distorted, and replacing the set fixes the issue ...for a while.
I cannot find any reason for the failure...pressure spike? WHY? I have replaced and re-checked the expansion tank, pressure relief valve 2x, descaled and refilled the system with inhibitor, and most recently added a 1/32" thin gasket to the face of the exchanger to compensate for any distortion/dimension change....after a month of fine operation, client came home to a pool of water, AGAIN.
Since the pressure relief valve is set at 30psi (2 bar) and the system operates at 1 bar, the replaced and pressure adjusted expansion tank (12psi) should handle any pressure rises, right? And if not that, the relief valve should pop @ 2 bar.
So why does the pressure relief valve occasionally drip, and why does it blow the exchanger seals? Could I add another hard piped expansion tank in the line?
thanks for any insight. I plan to replace the exchanger, as the front sealing face seems not perfectly flat...maybe all caused by an overtorque in the past? the unit had been serviced before I came on the scene...
Thanks,
C
I cannot find any reason for the failure...pressure spike? WHY? I have replaced and re-checked the expansion tank, pressure relief valve 2x, descaled and refilled the system with inhibitor, and most recently added a 1/32" thin gasket to the face of the exchanger to compensate for any distortion/dimension change....after a month of fine operation, client came home to a pool of water, AGAIN.
Since the pressure relief valve is set at 30psi (2 bar) and the system operates at 1 bar, the replaced and pressure adjusted expansion tank (12psi) should handle any pressure rises, right? And if not that, the relief valve should pop @ 2 bar.
So why does the pressure relief valve occasionally drip, and why does it blow the exchanger seals? Could I add another hard piped expansion tank in the line?
thanks for any insight. I plan to replace the exchanger, as the front sealing face seems not perfectly flat...maybe all caused by an overtorque in the past? the unit had been serviced before I came on the scene...
Thanks,
C
0
Comments
-
are you pumping into the HX?
What size circulator, adding how much delta P?
Scaled or partially plugged HX?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements