Consensus on toe kick heaters
We are going to remodel our kitchen. Time is hard to come by so we are getting estimates. The kitchen currently has an 8 ft section against the back wall.
The contractor is suggesting a 4 foot section against the left wall near the basement and back door. I would have put it there myself regardless. It won't interfere with the doors.
And a toe kick heater under the cabinets we would add to the back wall. I am running fin tube at roughly 115 to 145 degrees. Do these units perform well at that temp?
Mad Dog_2
  • HomerJSmith
    HomerJSmith Posts: 2,837
    edited October 2019
    115 to 145 degrees? That is relatively cold for fin tube, but can be done. The baseboard has a thermodisc sensor on the tube that turns on the fan at a temperature at about 120 deg. You might have to change the thermodisc. You don't want to blow cold air as it is uncomfortable. Even 115 deg air might feel cold as it mixes with the ambient input air.
    Why are you running it so cold? You need a lot more baseboard to provide the BTU's into the room at lower tube temperatures. There is also the possibly of running out of heat energy when you start out at lower temperatures in which case you can boost the flow rate, but there are limits to that.
    Leon82
  • Leon82
    Leon82 Posts: 681
    I've dialed it in over the past two years with a condensing boiler. The heat is adequate.
    So the kitchen would have a 50% loss of fin tube but gain the kick heater.
    My original plan was to add the cabinets above the baseboard but then it would heat the cabinet
  • STEVEusaPA
    STEVEusaPA Posts: 6,505
    Is floor or ceiling radiant an option?
  • Not a fan (get it) of noisy toe kicks. How about some HO baseboard or panel rad sized to be of equal output of the BB you take out?
    Leon82
  • HomerJSmith
    edited October 2019
    I prefer the Turbonics Toester toekick heaters over the elongated cage fan types. I had to replace motors and and bearings in those and they are noisier. The Toester uses a radial fan much like a muffin fan found in computers, but larger of course. I find that they are quieter.
    Toekicks put a lot of BTU's packed into a small space.
    Leon82Long Beach EdMad Dog_2
  • Leon82
    Leon82 Posts: 681
    I was thinking that could be an option like the Smith heating edge
  • Leon82
    Leon82 Posts: 681
    Floor could be, probably a plate type
  • JeremyG
    JeremyG Posts: 18
    edited October 2019
    The house I moved into a couple years ago has a Beacon Morris K42 toe kick heater in the kitchen. I'm not impressed. The rest of the house is cast iron radiators sized for the house before it was insulated, so that means cool temps (110º) a lot of the heating season. The fan would almost never run until I put in the low-temp 'stat. Seems like the low fan speed doesn't move enough heat, and the high speed is annoyingly noisy. I intend to put in radiant floor heat to replace it, because it's not really adequate on paper and even less so in practice.
    markham56Leon82
    I’m having the same problem with a K120 in my 1928 house even with a low temp aqua stat. It just doesn’t stay on long enough to get the room warm.
    I remodeled the kitchen and removed the radiator in the hope of saving space and that the K120 would proved better heat. Any suggestions?
  • HomerJSmith
    edited December 2019
    The manufacturer will tell you the temperature that the fan kicks on at. On low temp sys, I have replaced the thermodisc to a lower cut-in (Make) thermodisc that worked great. On low temp sys, you might want to run it at a low blower speed.
    Leon82
  • MikeL_2
    MikeL_2 Posts: 561
    Maybe 4' of high capacity baseboard will be sufficient.
    How about a recessed convector if wall space allows? There is a vertical cabinet available for recess mounting a toe kick unit.
    Is there access below the kitchen? You could add a toe space unit after the fact if you find you need more heat.
    We prefer to install toe space units in interior cabinets so the unit discharges towards the exterior wall.......
    Leon82
  • tocker
    tocker Posts: 40
    Has anyone solved or has a better solution for the low water temp/fan noise conundrum on kick plates(?). I need to replace the second kick plate in my kitchen. My Lochinvar modulating boiler provides water temps between 100 and 140ish max. Usually it runs 110-120 degree water when outside temps are around 30. Any new ideas/recommendations?
    Steamhead Posts: 19,022
    Certainly. Put in a radiator to match the rest of the system.
    Semi-retired
  • TAG
    TAG Posts: 807
    open basement under kitchen for radiant ?
  • Mad Dog_2
    Mad Dog_2 Posts: 8,758
    Turbonics makes the best I have found. I installed one in my inlaws kitchen & it worked silently 27 yrs. This year it got noisy, but that's a vg run. If you're getting the kitchen, Radiant is your best choice. Mad Dog
