Steam Vacuum
donahueostrum
Member Posts: 1
I just installed a Weil McLain LGB 7 steam boiler to replace the same boiler I installed 18 years ago. The install went fine. It's a two pipe system in a large house. The only two vents in the system are located on two main returns back at the boiler. The vents are high capacity which I replaced. When I started the boiler I noticed it would create a vacuum and suck the water from gauge glass and turn off boiler on low water,once the system cooled down the water filled gauge glass and turn on boiler.The boiler I removed worked all that time and never had an issue like that. What Changed? Why would I need a vacuum breaker in system after all these years?All returns are newer and water is getting back to boiler? What am I over looking?Thanks,Joe
0
Comments
-
That’s not a vacuum, that’s surging. Sounds like you need to skim the boiler more. Have you skimmed it yet @donahueostrum?0