Heating System Retrofit
grrrdot
Member Posts: 10
in Gas Heating
Hi,
Looking to replace an old oversized boiler with a more appropriately sized mod-con. Additionally, the current system has performance problems; one zone too hot, one zone too cold and one zone just right.
Looking for some feedback / new ideas to improve performance when doing the boiler install.
This is in an old 1800 sqft brick row house, the building was gut renovated in the late 90's with an open floor plan so its laid out as three large rooms with a zone for each floor. Boiler is piped P/S with two secondary loops.
So, thoughts on setting up the boiler something like?
Looking to replace an old oversized boiler with a more appropriately sized mod-con. Additionally, the current system has performance problems; one zone too hot, one zone too cold and one zone just right.
Looking for some feedback / new ideas to improve performance when doing the boiler install.
This is in an old 1800 sqft brick row house, the building was gut renovated in the late 90's with an open floor plan so its laid out as three large rooms with a zone for each floor. Boiler is piped P/S with two secondary loops.
- Bottom floor/zone is a Concrete slab with two 1/2" pex loops. It uses its own thermostat and gets 120F water. This zone works great.
- Second floor/zone uses its own thermostat and is a mish-mash; a single large panel w/ TRV is in series with one loop of a two loop suspended 1/2" pex radiant floor. This zone is using zone valves to share the pump and mixing valve with the bottom floor, so it gets 120F water. This zone struggles to keep up and falls behind on colder days.
- Top floor/zone uses its own thermostat and has three panel radiators all with TRV. Residents have to leave the TRVs wide open or the system makes a lot of noise. This zone has its own pump and gets full temp water, 175F. Feeling is this zone is always hot.
So, thoughts on setting up the boiler something like?
- ODR curve to 160F for design day temp (17F)
- Top floor and second floor share a variable speed delta-p pump with two zone valves.
- Bottom floor continues with mixing valve at 120F and current pump.
0
Comments
-
First assure that the amount of heat emitters can meet the design day heat load. At the SWT you are considering.
It could b e the TRVs are installed backwards, they should be absolutely quiet.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements