Taco zone valves leaking through the seal.

Smoky
Smoky Member Posts: 1
I have had 3 seal failures in 6 months on a G3 valve. It’s a pump and dump system. I was thinking of replacing them with a V075T2G22A024Q4A1 Taco valve. Will this solve my problem

Comments

  • Please explain "pump and dump".
    Often wrong, never in doubt.
  • hot_rod
    hot_rod Member Posts: 14,562
    Maybe look at a ball valve type for pump and dump use. Here is an example of a Caleffi version 6442, we sell a lot for pump and dumps. Ball valves have a much higher flow (cv) and shutoff pressure rating. Most need power to open and close, they are not spring return. So a RIB relay needs to be added.

    Pump and dump uses well water pumped thru the HP then dumped down another well, or drainage when allowed. Often the same well pump that supplies the home or building. The DNR watches and regulated this type of system around here. the concern is oils getting into the aquafier.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • hot_rod
    hot_rod Member Posts: 14,562
    Maybe look at a ball valve type for pump and dump use. Here is an example of a Caleffi version 6442, we sell a lot for pump and dumps. Ball valves have a much higher flow (cv) and shutoff pressure rating. Most need power to open and close, they are not spring return. So a RIB relay needs to be added.

    Pump and dump uses well water pumped thru the HP then dumped down another well, or drainage when allowed. Often the same well pump that supplies the home or building. The DNR watches and regulated this type of system around here. the concern is oils getting into the aquifer.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Dave H_2
    Dave H_2 Member Posts: 423
    @Smoky
    Yes the V075T2G22A024Q4A1 Geo-Sentry is a ball valve style zone valve. They are designed for a Geo system and with this motor, you do not need a RIB relay for it close. There are two on-board capacitors, one for opening the valve and one for closing the valve. The closing capacitor gets a trickle charge while the motor is in the open position.

    Dave H