Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
N
JPL941
Member Posts: 51
Hello
0
Comments
-
-
Hello
0 -
So you already have a fairly new steam boiler. You wanted some hot water zones and for that you added a whole other boiler? If you want a good idea I would suggest you abandon the ridiculously oversized combi and put a hot water zone off of the steam boiler. Even if you were to use the combo for the entire house it’s probably 3-4 times oversized for the job.
Your concerns about leaking steam pipes are unfounded, unless your system is really messed up making tons of wet steam. Hard to judge unless you post pics of how you had it repiped.0 -
Hello
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements