N
JPL941
Member Posts: 51
Hello
0
Comments
-
-
Hello
0 -
So you already have a fairly new steam boiler. You wanted some hot water zones and for that you added a whole other boiler? If you want a good idea I would suggest you abandon the ridiculously oversized combi and put a hot water zone off of the steam boiler. Even if you were to use the combo for the entire house it’s probably 3-4 times oversized for the job.
Your concerns about leaking steam pipes are unfounded, unless your system is really messed up making tons of wet steam. Hard to judge unless you post pics of how you had it repiped.0 -