I put a new ZVC405 on my 5 zone with priority on my radiant system. The main circulator and boiler fires as soon as heat is called by the thermostat before the actuator opens. The causes a hammering in the pipes till the valve fully opens. Do I need to put a switching relay of some kind of delay timer to eliminate this problem.
0
Comments
-
Do you have thermal actuators with end switches? Unless an end switch connection is jumped, the valve end switch should call on the circulator?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod, the actuators are wired as they were originally, 2 wires with the end in controller unit looped 3&4. The actuators do have 4 wires which I assume was for the end switch but they had them snipped off, not sure why.0
-
The end switch wires need to be connected to allow it to work properly, the pumps should wait until the valves are open, at least partially, before any circulators start spinning.
With jumpers as you indicated, yes the pumps will start as soon as the T-stat calls any zone on, not ideal
There are some relays that work on time delay instead of end switch closure, I don't know that that model has that feature?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements