Fuel smell discharge from the draft control
hosviolin
Member Posts: 1
in Oil Heating
Every once in a while partially burned fuel oil odor comes out of the draft regulator when the furnace starts. (Weil McClain boiler, Beckett burner, Field Controls "R-C" calibrated draft control, all c. 1990) One time I witnessed a puff of smoke coming out of the draft regulator when the furnace started. The odor is not unlike driving behind a diesel powered truck that is most likely in need of a tune up.
My furnace tech seems not to be able to pinpoint the problem. Is it possible that more outside air needs to be available for the burner? I imagine more than just diesel odor is getting into the air in my basement.
Any ideas would be helpful.
My furnace tech seems not to be able to pinpoint the problem. Is it possible that more outside air needs to be available for the burner? I imagine more than just diesel odor is getting into the air in my basement.
Any ideas would be helpful.
0
Comments
-
The risk is Carbon Monoxide poisoning.
You IMMEDIATLY need a new technician and a chimney sweep to check the flue.
Failure to take care of this could be deadly. Get a co detector down there.
It could be a blocked chimney,
dirty boiler
mis adjusted burner
or any number of things
This is what we read about in the news, Don't become a statistic.
I would shut the boiler down1 -
I would check the cut off on the oil pump. If it's not holding pressure properly after shut down you will get oil dribbling out of the nozzle causing soot, CO and smoke on start up. I prefer oil pumps with a solenoid valve. Is your team have using a digital combustion analyzer to tune your burner? I hope so. It should be pretty easy to check using an analyzer and pump testing manifold.2
-
There was an error rendering this rich post.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements