Genoni failure solution
Henry
Member Posts: 998
We have noticed a number of genoni heat exchanger failures in apartment blocks that have had to drain the system for repairs. The fresh water causes corrosion and iron oxide sludge (manganite). For up to 1 million BTU, it is a 1 inch bypass system with a Dirtmag and a 20 inch 5 micron bag filter plus a flow meter. Up to 2 million BTU it is a 2 inch Dirtmag and a 40 inch 5 micron bag filter plus a flow meter. The flow rate for the 1 inch is 10 GPM and an UP15-42 is satisfactory. The 2 inch is at 45 GPM using an UPS26-150. The enclosed sketch shows an error by our tech, it is not 5 GPM for the 1 inch. It is in French as most of our plumbers are French speaking. The enclosed pictures show a sample of boiler water that was magnetised. The iron particles fell to the magnet. The yellow water was the same system after two months of bypass filtration. It is a relatively inexpensive insurance for the boilers.
0
Comments
-
The Dirtmag is a great product, I'm always surprised at how much magnetite gets blown out after I remove the magnet.
How often do you need to replace the five micron bag filter?0 -
-
Is there a differential pressure monitor or gauge to determine when the bag needs to be changed?Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
good thought, a pressure gauge on the filter would be an indicator, like a pool filter typically uses.Solid_Fuel_Man said:Is there a differential pressure monitor or gauge to determine when the bag needs to be changed?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
The best solution is not to use a boiler with a Giannoni heat exchanger in the first place. Then, all these band-aids aren't needed.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Nothing at all wrong with Sermeta HX as long as they are pumped properly, have good water quality and adjusted and cleaned on the burner side. Mounted improperly in plastic enclosures didn't help their longevity
Still plenty being used in single and stacked versions. Some long experienced wholesalers tell me fire tube style are failing as if not more often than the Sermeta style.
https://sermeta.com/en-us/Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
There is a flow meter (débitmetre) to tell the user when to replace the filter or to purge the dirtmag. We have Genoni/Sermeta boilers running for over 12 years with relatively low maintenance. But if one not installed properly with the right pipe size or pump, it can fail within 5 years. A lot of installers look at the boiler connection size and not the required flow rate size. It is like connecting a 500,000 BTU flat plate heat exchanger that has 1 inch connection and use 1 inch to the boiler! 500,000 BTU requires 2 inch! Even if one sizes everything right but there are frequent emptying of the system to repair leaks, the boilers will pack up due to the fresh O2 and water with sludge. The system that I have shown is for existing installations. New installations can have a Dirtmag of the proper size instead of a Y strainer.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements