C Wire Gas Boiler Wiring
bbnyc
Member Posts: 1
in Gas Heating
Hi,
I have an old thermostat with only 2 wires connected to my Weil-McLain CGA Series 2 boiler. I would like to replace it with a Nest thermostat. I need to add a C-Wire in order for it to work. Luckily, the cable coming from my thermostat already has a 3rd wire that I can use. I just need to find where to connect the C wire on the boiler side. In attached picture, blue pen drawing shows existing wirings. The Low Water Cut Off has 4 wires, and one is already connected to the C Common terminal. Can I just connect my thermostat’s C wire to the same terminal? (Green pen in drawing) Thanks!
Aquastat is I believe Honeywell L4006E1067. Low Water Cut Off is GuardDog LB-24E. Orange and blue nuts connectors in picture connect all the above limits + thermostat in series to the thermostat connector on boiler. All other limits and external devices are mounted per manual diagram.
Thanks !
I have an old thermostat with only 2 wires connected to my Weil-McLain CGA Series 2 boiler. I would like to replace it with a Nest thermostat. I need to add a C-Wire in order for it to work. Luckily, the cable coming from my thermostat already has a 3rd wire that I can use. I just need to find where to connect the C wire on the boiler side. In attached picture, blue pen drawing shows existing wirings. The Low Water Cut Off has 4 wires, and one is already connected to the C Common terminal. Can I just connect my thermostat’s C wire to the same terminal? (Green pen in drawing) Thanks!
Aquastat is I believe Honeywell L4006E1067. Low Water Cut Off is GuardDog LB-24E. Orange and blue nuts connectors in picture connect all the above limits + thermostat in series to the thermostat connector on boiler. All other limits and external devices are mounted per manual diagram.
Thanks !
0
Comments
-
Follow a green wire and send the common from the thermostat to the ground screw.
There was an error rendering this rich post.
0 -
I have the same need for C wire. Can you post where to connect for C wire?0
-
@bbnyc, your boiler has two black wires that go to the R and W terminals on the thermostat. If Weil McLain were user friendly, one of those black wires would be Red and the other would be White. But that would make it too easy. One of the black wires should be red and the other should be the white. You may need a multi-meter to determine which is which. It is not important if you don’t use a thermostat that requires a C (common) wire.
By using a thermostat that requires a common , it now is important to know which is which.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
It appears that the hand drawn diagram you made will operate properly. If the L4006 or the LWCO ever trips, the Nest will show an error message “ no power to thermostat “. I think it is E72 but I’m not 100% sure of the error number.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements