Beckett NX-spline nut blues
Options
STEVEusaPA
Member Posts: 6,506
So is it me? Or has anyone else have this issue?
How do you adjust the air on a NX burner while it’s running? In theory, loosen the spline nut, adjust the head by turning the screw, right?
Should be simple enough per the instruction. But twice now I’ve noticed the spline nut cannot be loosened to allow air adjustment with the nozzle adapter connected to the fuel pump. The nut that connects them bottoms out on the spline nut, so you can’t loosen the spline nut. Doesn’t do it on an AFG.
I ended up leaving the spline nut off and using an e clip.
Am I completely missing something and having a brain fart, or is this just bad design?
Thanks
Steve
How do you adjust the air on a NX burner while it’s running? In theory, loosen the spline nut, adjust the head by turning the screw, right?
Should be simple enough per the instruction. But twice now I’ve noticed the spline nut cannot be loosened to allow air adjustment with the nozzle adapter connected to the fuel pump. The nut that connects them bottoms out on the spline nut, so you can’t loosen the spline nut. Doesn’t do it on an AFG.
I ended up leaving the spline nut off and using an e clip.
Am I completely missing something and having a brain fart, or is this just bad design?
Thanks
Steve
steve
2
Comments
-
I've never had a problem. Maybe the flare nut on the nozzle line has threads that are too deep.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Steve, you aren't crazy. Have to loosen both to adjust.To learn more about this professional, click here to visit their ad in Find A Contractor.1
-
Thanks.Robert O'Brien said:Steve, you aren't crazy. Have to loosen both to adjust.
Hey Beckett, can you just make the nozzle line portion with the threads 1/4" longer?
steve1 -
That seems to be it too. But it seems to me to only happen on newer burners, as I don't remember this being a problem on them when I first started working on them. Maybe the whole adjustment/head mechanism is a little thicker on the newer ones?Steamhead said:I've never had a problem. Maybe the flare nut on the nozzle line has threads that are too deep.
steve0
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements