Lumpy fostapex?
theguynextdoor
Member Posts: 2
Hi all
New here..
Local plumber here in Ma..
I have an oil fired hydronic system..system was here before we purchased
They used Viega fostapex to connect the supply and return lines to the boiler to existing blk pipe and baseboard..this morning I had a zone valve fail and while inspecting I noticed a bulge/split in one of the supply lines near the boiler(no leak) and then upon further inspection noticed some of the fostapex appears to be lumpy? Any advice,suggestions etc..is appreciated
New here..
Local plumber here in Ma..
I have an oil fired hydronic system..system was here before we purchased
They used Viega fostapex to connect the supply and return lines to the boiler to existing blk pipe and baseboard..this morning I had a zone valve fail and while inspecting I noticed a bulge/split in one of the supply lines near the boiler(no leak) and then upon further inspection noticed some of the fostapex appears to be lumpy? Any advice,suggestions etc..is appreciated
0
Comments
-
got a pic?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
Freeze up between the layers of the fostapex??? Please provide a few pictures. I have never seen what you are describing.0
-
Thank guys..Was thinking from the water temp possibly? I believe its rated for 180f ?
Pictures below..hope it worked. Anyone see them?0 -
Looks like the fostapex is doing its job. Wow! No leaks! Really?!
In the first and third pictures it looks to me as if water some how got between the layers.
The third picture might be from when the pipe was uncoiled and had some ripples in it from the coil.
Never saw the results of the first and second picture. I am looking forward to what others will have to say.1 -
Different about FostaPex is that it has a standard full size pex SDR-9 tube I believe the inner tube is an oxygen barrier tube. The aluminum is just a protective layer, additional O2 barrier with a plastic over it, not really part of the integrity of the tube like aluminum in PAP. That is why the OD is larger than other PAP.
It does look like something caused the pex tube to expand, freezing, being run over?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
-
Had a similar situation, we determined at some time the water temp went above the temp rating on the tubing due to a bad aquastat. The temp gauge your looking at may not be accurate.0
-
The Viega site indicates that is hydrostatically tested to 400F? Rated like other pex the higher the temperature the lower the pressure, something like 180F at 100 psi seems to be what everyone lists.billtheplmbr3845 said:Had a similar situation, we determined at some time the water temp went above the temp rating on the tubing due to a bad aquastat. The temp gauge your looking at may not be accurate.
I think the legal folks start to squirm when you mention listing products over 200F or so, even if the product can easily handle it.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements