I had MassSave out for an energy audit and they did a combustion analysis on my 35+ Penco 200K Steam boiler. They said it was operating safely but mentioned the exhaust temps were over 500F...what does this mean? Anything to be concerned with?
Boiler is serviced yearly by someone from this board.
Boiler is serviced yearly by someone from this board.
0
Comments
-
That's bit high. Depending on what else is going on combustion wise I wouldn't worry too much. If I was servicing that boiler I'd try and find out why is that high. Did you get any more numbers from MassSave?Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker0
-
I'd check to see if the burner is over-fired. If it isn't, there may not be much you can do- some of these older boilers were pretty inefficient.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Depends. I wouldn't consider 500 really excessive. I would consider 600 excessive. Next time it's serviced I would check the combustion efficiency and firing rate. Doesn't sound like a serious issue.
Is this gas or oil?0 -
Could also be too much draft.
There was an error rendering this rich post.
0 -
Gas with a draft diverter draft probably not an issue but oil it certainly could be an issue. Combustion test0
-
I’ll see if I can get the combustion numbers when he emails me tonight.
It is natural gas. Actually 1970 so quite old.
He was testing it at worst case draft scenario, baths fans exhausting, dryer, and large Pro range hood on max.
My guy who serviced it in the fall did mention he tweaked the firing.0 -
Is that gross or net?
Nice job running all exhaust to check for back draft but did he calculate the free air needed for proper combustion?0 -
Not sure, he just mentioned it offhand.
That is gross 199k/152k.
My sticker from servicing says 8.6 O2 with 495F stack temp so I guess that’s how he wanted it set up.0 -
Those are good #s for gas. Not the best if it's oil. We still don't know do we??
If it's gas your ok0 -
If the CO is ok0
-
It’s gas. He said CO2 passed fine. Sounds like I’m all set. Thanks!0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements