Doyle 2A vacuum valve
Doester
Member Posts: 17
Is there any difference between a “vacuum valve” and a regular air vent? I was going to replace this with a Hoffman 1A so I could slow it down. Single pipe steam system.
Thanks!!!
Thanks!!!
0
Comments
-
There is a difference @Doester. Vacuum vents had check valves that enabled the system to go into vacuum after the air had been vented. I say HAD because they don’t make vacuum vents for radiators anymore. So, the Hoffman 1a would be fine.1
-
Thank you!!!0
-
Do the rest of your radiators have vacuum vents? How about the vents at the ends of the steam mains?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
No, only 2 vacuum vents out of 16 radiators. And the main vents were “Hoffman float quick air vents”. I’ve replaced them with bigmouths. Thanks!0