Separate Indirect DHW signal from Taco SR503
I am really new to all these. I have been reading posts in this great forum but unfortunately wasn’t able to find a lot information about Hydrolevel.
Many thanks in advance.
Comments
-
With the Economy feature turned on, my boiler’s high temperature limit various between 145F to 170F, the low temperature limit seems to be consistent 125F. Though my DHW is wired correctly to the priority zone in Taco SR503, the 145F boiler water takes too long to satisfy the target temperature which is now set at 130F. It was originally set to 140F and that took even longer. If the Economy is bypassed, the boiler will run at full power. The high will be 180F and low will be 170F.0
-
Hi Yuwei, your zone 3 priority is turned off on your board. I assume zone 3 is your DHW tank.
with that "zone 3 priority" turned off it is not treating zone 3 as a priority but as another zone. turn it on and you should get better DHW recovery time.0 -
Do you have that relay that you posted on the boiler?
If so the indirect thermostat is
in cable 2. Green and white.
I've never wired the 3000 but it looks like an isolation relay is needed.
You'll have to find out which is the load side of the indirect thermostat. Green or white? The load side will energize a (field supplied) 24v, single pole N.O. open relay as well as completing the circuit back to the 3000. The N.O. contacts will go to R-W on zone 3 for the indirect.
Set your economy. You can leave the priority switch off on the SR503.
I downloaded the 3000 manual. Unless I'm not seeing it, they dont show that which is a shame.0 -
Hi Jellis, the Priority switch in Taco was turned on and working fine. When DHW calls for heat, the rest zones won't run. The problem is Hydrolevel 3000 cannot tell if it's a priority heat call or a regular call, hence it's running on a lower temperature.Jellis said:Hi Yuwei, your zone 3 priority is turned off on your board. I assume zone 3 is your DHW tank.
with that "zone 3 priority" turned off it is not treating zone 3 as a priority but as another zone. turn it on and you should get better DHW recovery time.0 -
Hi HAVCNUT,HVACNUT said:Do you have that relay that you posted on the boiler?
If so the indirect thermostat is
in cable 2. Green and white.
I've never wired the 3000 but it looks like an isolation relay is needed.
You'll have to find out which is the load side of the indirect thermostat. Green or white? The load side will energize a (field supplied) 24v, single pole N.O. open relay as well as completing the circuit back to the 3000. The N.O. contacts will go to R-W on zone 3 for the indirect.
Set your economy. You can leave the priority switch off on the SR503.
I downloaded the 3000 manual. Unless I'm not seeing it, they dont show that which is a shame.
Thanks so much for the answer, I don't have the relay yet but I guess it is a normal N.O relay and can be easily found in ebay, am I right?
My Cable 2 is slightly different to what's described in the latest manual. It doesn't have Green and white wires but two Brown wires. I called the Hydrolevel support and he said it's the same. Is that right?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements