Boiler Turn Down Ratio

Le John
Member Posts: 241
What do the turn down numbers represent on a 90,000 BTU Combi Boiler? 3.8:1 / 1.2:1
0
Comments
-
A 3.8:1 ratio is 26% (1 divided by 3.8). 26% of 90,000 BTUs is 23,684 BTUs.Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385