How to balance a pex manifold?
Ed Lentz_2
Member Posts: 158
I have a 4 zone pex manifold. It is a Stadler Viega Brass manifold.
I have poor heat transfer in two of the zones. They are fairly the same length, if I remember right. Put the system in over 15 years ago. The controller is a Stadler Basic (Rebranded Tekmar I am told). I did some crude temp measurements using a instant meat thermometer on the Pex itself near the manifold coupling. Here is the results. In the temp difference between source and return
Zone 1 28 degrees
zone 2 5 degrees
Zone 3 3 degrees
Zone 4 10 degrees.
The zones that are the coldest are 1 & 3
I have searched all over on balancing, but nothing specific on this manifold. Is it just a matter of adjusting the valves on the source for each zone? I have no way to ascertain the flow rate. Would it be possible to have an air bubble in a zone or two? That would keep the circulation to a minimum wouldn't it? I do have air traps
installed. One other question, the Oventrop on the right. What is it's purpose? When I installed this I had the help of a Master Boiler Installer. He spent hours drawing up my system , sold me the stuff and stood inspection with me. He has since past away so I am left to some of my own failing memories (
Thanks for any ideas
I have poor heat transfer in two of the zones. They are fairly the same length, if I remember right. Put the system in over 15 years ago. The controller is a Stadler Basic (Rebranded Tekmar I am told). I did some crude temp measurements using a instant meat thermometer on the Pex itself near the manifold coupling. Here is the results. In the temp difference between source and return
Zone 1 28 degrees
zone 2 5 degrees
Zone 3 3 degrees
Zone 4 10 degrees.
The zones that are the coldest are 1 & 3
I have searched all over on balancing, but nothing specific on this manifold. Is it just a matter of adjusting the valves on the source for each zone? I have no way to ascertain the flow rate. Would it be possible to have an air bubble in a zone or two? That would keep the circulation to a minimum wouldn't it? I do have air traps
installed. One other question, the Oventrop on the right. What is it's purpose? When I installed this I had the help of a Master Boiler Installer. He spent hours drawing up my system , sold me the stuff and stood inspection with me. He has since past away so I am left to some of my own failing memories (
Thanks for any ideas
0
Comments
-
If it has worked in the past, I’d suspect that Oventrop not opening fully. I think it is a master ZV for the entire manifold, or is it an adjustable TRV.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It is a TRV But only moves from 1 - 3 Never was to clear on ist purpose there0
-
How does that valve open, on a downward force or up?0
-
So it has a sensor into the room? Higher number typically higher temperature. Remove the head and it should be wide open, full supply temperatureBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I removed the TRV and the house is 5 degrees warmer this morning. This is a good thing. I also opened all the valves to allow full flow on all the zones.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements