Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Vitoflame 100 Chassis burner
Jay_insula1203
Member Posts: 21
Had a service call on a Vitola 200 with a Vitoflame 100 Chassis burner, found the burner running with no flame and oil coming out of the chamber. In all my years of service I have never have seen this before, after cleaning up the oil (big mess) I tested the control and it shut down every time I removed and blocked the Cad cell. I am not going to put this boiler back in service until I obtain a new primary control. Has anyone experienced this before with this burner ? Thanks for any input.
0
Comments
-
I’ve installed a few chassis’s in my day, that’s a new one
I agree, get a new primary control on there and word your invoice carefully. Next step is a new burner (if it happens again)0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements