feeding with a MM67, new install

GWGW Posts: 3,392Member
So I finally have a boiler with a MM67 and I need to feed it, anyone have a good-better-best way to do this? A few weeks ago I had issues with overfilling and @Steamhead gave me some tips. This is a little different- when i set up the TDC should i just change the circuit to 24V and do a 24v feeder? Running a TDC with line seems more cumbersome. Thanks for any comments
Gary Wilson
Wilson Services, Inc
Northampton, MA
www.wilsonph.com
[email protected]

Comments

  • SteamheadSteamhead Posts: 12,868Member
    If the 67 is wired 120V, I'd use a VXT-120, add the necessary switched wire back to the junction box and run a 3-wire BX cable from there to the VXT.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • GWGW Posts: 3,392Member
    Ok cool so yes or no on the time delay? Or, is it the SG400 that requires the TDC?
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    www.wilsonph.com
    [email protected]
  • GWGW Posts: 3,392Member
    I think I’m confused. A few weeks ago it was new style low-water cut off with oldschool Feeder, this time it’s old style LWCO with the new feeder. Got it. I’m making it more complicated than it is thanks for the advice