Trying to get a Taco RMB working properly. Only the top pump is working the bottom is cold and and. It working? I have the Manual switch on and still nothing. Could the pump just be frozen and just needs loosening and cleaning ? We just recently had a new well pump put in and had sediment in all the faucets etc in the house from doing so.

Comments

  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Is this in a heating application, as in with a boiler? If so your well water should have nothing to do with it. How long have you left the manual switch on? Does the bottom motor even get warm after 15 min with the switch on?
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Joe Mattiello
    Joe Mattiello Member Posts: 719
    Hi CFPcash
    Bottom pump is a 006 used as an injection pump, and top is a 008 system pump. Using the manual switch is a good way to circumvent the control, and run both pumps manually. If the pump is not running, usually you can tell by putting the blade end of a screwdriver on the motor, and butt end to your ear to magnify the impeller turns. If nothing, you might have a bad cartridge 005-020RP. if the motor is hot, and it's drawing approximately 1.5 time nameplate amps, it's a failed cartridge.
    Call Tech support at 401-942-8000 for additional support.