Goodman Model #PGB 042100-1
Comments
-
Put a jumper wire between R W at the furnace. If it starts, check wires/batteries/replace stat.0
-
so i have 26 volts on the w to r and also from common to w. the thermostat is a mechanical and uses no batteries.0
-
You should have 24 volts nominal (your 26) from common to red at the control board.....do NOT jumper those together.
But do jumper the R to W, that is the switching action that your thermostat does. Heat then??0 -
-
Agree, I was under the assumption the wires were disconnected already.0
-
Damn tunnel vision any way. I replaced the thermostat about 6 months ago. It had a programmable one that quit me during the warm months. I replaced it with a Honeywell mechanical (cheapy), so I just figured it was good and had not tried jumping it. After all it was replaced just 6 months ago and I assumed it to be good. Well the jumper got some heat going so now I feel like a total ****. Will prolly end up replacing the smart valve since it is low on voltage coming out to ignitor/flame rod assembly. Thanks for the kick start to pull my head out and look around. After all, it was daylight!-1
-
> @OleBones said:
> Damn tunnel vision any way. I replaced the thermostat about 6 months ago. It had a programmable one that quit me during the warm months. I replaced it with a Honeywell mechanical (cheapy), so I just figured it was good and had not tried jumping it. After all it was replaced just 6 months ago and I assumed it to be good. Well the jumper got some heat going so now I feel like a total ****. Will prolly end up replacing the smart valve since it is low on voltage coming out to ignitor/flame rod assembly. Thanks for the kick start to pull my head out and look around. After all, it was daylight!
I enjoyed reading this post and I'm glad you got the heat working. Do yourself a favour if you are investing in a new smartvalve, buy a new igniter/flame sensor with it.
With those new components it should keep the burner section of the furnace reliable for several years.
I'm guessing as an owner of a furnace with a smartvalve that you wouldn't want one on your next furnace. I never liked them much. I hate when I need one and I have universal gas valves on the van that I can't use.0 -
You can bet your bippy, you couldn't pay me to have another furnace with a smart, high dollar piece of crap, valve. I just finished replacing a smart valve on a water heater that was less than 3 years old. Looks to me as long as Honeywell has been in business, they would be manufacturing more reliable equipment or at least providing a better warranty on their POS valves!SuperTech said:> @OleBones said:
> Damn tunnel vision any way. I replaced the thermostat about 6 months ago. It had a programmable one that quit me during the warm months. I replaced it with a Honeywell mechanical (cheapy), so I just figured it was good and had not tried jumping it. After all it was replaced just 6 months ago and I assumed it to be good. Well the jumper got some heat going so now I feel like a total ****. Will prolly end up replacing the smart valve since it is low on voltage coming out to ignitor/flame rod assembly. Thanks for the kick start to pull my head out and look around. After all, it was daylight!
I enjoyed reading this post and I'm glad you got the heat working. Do yourself a favour if you are investing in a new smartvalve, buy a new igniter/flame sensor with it.
With those new components it should keep the burner section of the furnace reliable for several years.
I'm guessing as an owner of a furnace with a smartvalve that you wouldn't want one on your next furnace. I never liked them much. I hate when I need one and I have universal gas valves on the van that I can't use.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements