Remote bulb TRV
Solid_Fuel_Man
Member Posts: 2,646
I'm looking to control a reheat coil in ductwork after an ERV. This would be if the supply air from the ERV drops below say 55 degrees. Coil is 60,000 btu water.
I was looking at a 3 wire floating valve and a Honeywell PID controller, but have been intrested in a simple non-electric TRV idea, much less money too. Remote bulb in duct after coil, head set to 55F and let it go.
I was told however that it wouldn't last the test of time. I have no experience with this type of setup so I'm asking here.
Looking at Honeywell V110E1012 valve and T100F1395 actuator.
I was looking at a 3 wire floating valve and a Honeywell PID controller, but have been intrested in a simple non-electric TRV idea, much less money too. Remote bulb in duct after coil, head set to 55F and let it go.
I was told however that it wouldn't last the test of time. I have no experience with this type of setup so I'm asking here.
Looking at Honeywell V110E1012 valve and T100F1395 actuator.
Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements