Dual Roth Tanks not equalized
Tank A currently reads 3/4 full. Tank B is at or slightly below 1/8 full. When I went down to check the oil I was expecting both to read somewhere around 1/2 full. Knowing how low tank B is and how full tank A is, this has been going on for quite a long time (it's been warm weather and no heat used other than hot water up until a month ago). I suspect the problem happened about a month after my last fill.
First question (see attached picture): What is this valve called?
It is very clear that it has an inlet for fuel that is drawn from the other tank, as well as drawing fuel from the tank it is located on top of. It has a single outlet for fuel that goes to the furnace, and a return inlet (outlet?) that is unused. The lever on the top is in the up position currently. I believe it should be in the down position, and might actually be the root of my entire issue. If I am correct that it should be in the down position, what could cause it to move to the up position without any outside disturbance?
Second question: Is it safe to have my tanks filled, and will they be equalized after the fill?
Third question: if the answer to the first question does not provide my fix, what should I be looking at as the issue? What is the order of steps in troubleshooting?
First, the lever must be up.
Tank A has a clogged, or broken pick up line and is not drawing fuel.
That tank valve and float type pick up tubes were abandoned by Roth some years ago.
My advice and how I always did it,
1/2" L copper pick up tubes.
1/2" copper coated oil line out of each tank with inline ball valves so you can isolate each tank, and clear each line individually if needed.
Tee them together, and continue 1/2" oil line to the equipment.
Most recommended putting an oil filter at the tank(s).0 -
DO NOT HAVE AN OIL COMPANY FILL THOSE TANKS!!
Sorry for the caps, but if they try to fill you will spill oil. They won't equalize on their own and you will have a disaster.
Here's the fix:
Never use the manifold fill, for the very reason you encountered. You can Tee the vents together, each with their own whistle, but 2 fill lines, one per tank.
I'm pretty adamant about this, regardless of what any manufacturer will argue.
They will never always fill equally, so they will never be at the same level
They will never always draw down equally, so they will never be at the same level.
And therefore, re-filling them risks a catastrophe, which by your diligence you will now hopefully avoid.
If I were there, I would re-pipe the 2 fills, then each tank is filled separately until the whistle tells you to stop.
If you don't want to do that, someone is going to have to equalize the volume of those tanks.There was an error rendering this rich post.
The tanks will equalize when pulled into a vacuum. When I worked at an oil company they had (2) 20,000 gallon tanks buried in the ground. They had a 4" common suction line coming from the tanks to a large pump which went to an overhead pipe rack to fill truck with. The tanks were in the ground so it was suction lift.
I always figured the tanks were connected across the bottom underground (which is illegal) but I was told with a vacuum on the suction line they would equalize, just like a syphon.
I saw trailer loads of oil dumped into the same tank and it never overflowed always equalized as fast as they filled it1 -
I don't believe the problem in this case is the fill and vent and equalizing.
The pick up line on tank A is broken. Unscrew the top and shine a flashlight in there. The plastic tube will be floating there like a dead eel.0 -
Or the valve is closed on tank A.0
I agree pick up line not working tank can't equalize. Tank that is low would have pick up line issue0
Are you guys saying with one tank at 3/4 and the other below an 1/8th, that filling these tanks won't cause a spill?
I'll take any bet, for any amount. Save some of your money for the cleanup.
I agree the immediate problem is the something in the pickup, but no way should the H/O get a delivery until those tanks are equalized. Being that there is going to be some work done on the tank system anyways, I'd change to 2 fill pipes, no equalizer, and pipe the pickups with copper, following manufacturer's directions.There was an error rendering this rich post.
I dont know @STEVEusaPA. Your probably right but with a Roth, I'm in for a cool $1.00.
I dont know from experience, just what I see in the field.
I've never installed twin Roths so I dont know the innards of the (dual) fill.
I just have never encountered a problem calling in for a drop when the tanks aren't equalized. Sometimes empty vs full. Pump it slow? I never delivered so again...
Even on steel tanks your saying (or not) dont- fill on one tank, 2" crossover, and vent the other?0 -
This is how I've repiped the oil line(s) after removing the Roth float type.
1/2" L pick up, no soft copper sleeves through.
1/2" gal. out the top of the bushing. Go to 1/2" coated oil line with a flare ball valve so you can isolate between the tanks, and valve off the oil in the suction line.
The 1/2" L pick up can be also be easily removed. Break a flare, unscrew the bushing and pull it out.
On the ground or up, over, and down, I sleeve the suction line through 3/4 seal tight conduit.0 -
DO NOT I REPEAT DO NOT PUT ROTH TANKS INTO A VACUUM, THEY ARE PLASTIC LINED TANKSEBEBRATT-Ed said:The tanks will equalize when pulled into a vacuum. When I worked at an oil company they had (2) 20,000 gallon tanks buried in the ground. They had a 4" common suction line coming from the tanks to a large pump which went to an overhead pipe rack to fill truck with. The tanks were in the ground so it was suction lift.
I saw trailer loads of oil dumped into the same tank and it never overflowed always equalized as fast as they filled it0 -
You won't believe what I found..........THE MANUAL WRITTEN BY THE PEOPLE THAT MAKE THE TANKS...........page 25, dual tank installation,,,,,,,, there is only one way to do it, by code and manufacturers directions
http://www.roth-usa.com/PDF_Download_Files/DWT Installation Manual 2017.pdf0 -
Fuel Supply Piping
1. Piping the fuel supply on a multiple Roth EcoDWT plus 3 installation is done
with the either copper tubing or black iron pipe.
2. Each Roth duplex bushing is equipped with two brass slide through
compression fittings for hard and soft copper. Feed the copper through the
fitting. Position the tubing 1” - 2” above the bottom of the tank to avoid getting
debris that might have settled in the bottom of the tank in the feed piping. The
compression fittings are then tightened.
3. When piping with black iron, the compression fittings are removed and 3/8”
or 1/2” pipe is threaded into each side of the duplex bushing. If the required
piping is greater than 1/2” a 2” die cast adapter and appropriate reducers can
be used in place of the duplex bushing. The adaptor must be purchased in
addition to the one supplied with the tank.
4. The piping configuration is known as “equal manifold” and requires balancing
the suction in the supply line and the flow in the return line (if used) equally
across all the tank connections. (see figure 5.5)
5. When done properly, the oil in each tank will be drawn out at the same rate,
keeping the same quantity of oil in all the tanks.
6. The interconnected piping also results in the oil levels equalizing in all the
tanks after the shutdown of the burner pump(s) by allowing the oil to siphon
from one tank to the other until all are at the same level.
7. The manifold assembly requires equal length piping coming out of each tank
to a common tee to balance the suction and return flow. As more tanks are
added to the installation, more tees are needed and the resulting piping will
resemble a pyramid in design.0 -
I don't understand your post. Are you shocked/amazed that you found the manual?GBart said:You won't believe what I found..........THE MANUAL WRITTEN BY THE PEOPLE THAT MAKE THE TANKS...........page 25, dual tank installation,,,,,,,, there is only one way to do it, by code and manufacturers directions
''manufacturers directions" state you can pipe it individually or with the manifold.
I'll never use the manifold for fills, and to avoid problems with too many proprietary plastic parts, I pipe the lines to the burner in copper.There was an error rendering this rich post.
1 -
The Equal Manifold stays at the Roth factory. Copper to an evenly spaced tee with isolation valves.
See ^^^ 11-5.
Critiques?0 -
@GBart
I think I misspoke or in this case miswrote.
This is what I was getting at. 2 suctions lines one from each tank teed together with the common line going to the burner. Once the system is primed and air free the burner will pull a vacuum on the 2 oil lines. If the oil level in one tank is higher than the other the burner will pull from the higher level (path of least resistance) When the burner shuts down oil will also syphon from the higher tank to the lower tank until equalized. Just like syphoning a gas tank.
Reading my post from 11/4 I didn't mean to say 'pull the tank into a vacuum" I was thinking "pull the oil lines into a vacuum1 -
I was being sarcastic, I have yet to see hardly anyone go to the manual, refer a DIY to the manual, most problems are solved there, time is saved there, time is money, when you encounter a problem go to the factory manuals, they built the stuff, they engineered it, they wrote the troubleshooting procedures, in some cases a technician may have found an answer and say "the factory said this, but this works better, or the factory rep came out and said these changes were made" all of this flying by the seat of the pants and opinions doesn't seem logical, eh?STEVEusaPA said:
I'll never use the manifold for fills, and to avoid problems with too many proprietary plastic parts, I pipe the lines to the burner in copper.2 -
not necessarily here but all over, we've become this opinionated nation where facts don't matter just opinions, if someone or a DIY posts a q here they get 17 different opinions instead of a very simple check the factory spec's, it kind of blows my mind how manufacturers spend all this time and money engineering and writing manuals to help people and save time and cover their butt and no one refers to them, if you install dual roth tanks and expect them to draw off the top equally you'd better set it up exactly like they say toHVACNUT said:@GBart
Which "flying by the seat of the pants and opinions" are you referring to?2 -
@GBart...huh? Don't lump me in with your political nonsense.
The OP wanted to know why his tanks weren't equalized, what he should do to fix it, and should he fill the tanks. I think between my first answer and @Hvacnut 's first answer it's pretty much covered.
Maybe we can ask to change the name of the website to 'dontAskUsReadTheManual.com? Then no one has to give an opinion...just 'facts'.
By the way, I'm not doubting the install isn't correct, according to the manual. I just don't install it that way for the reasons I stated early, and the possible situation that is occurring with the OP.There was an error rendering this rich post.
1 -
Let's get back on topic. Thank you.
President
HeatingHelp.com0 -
Yes @GBart you are 100% correct. The manuals were printed for a reason. I still have some like the one below, a crate of tech manuals between the seats of my service van, and my phone weighs a s*!t ton from all the pdf downloads.
However,
This thread in particular is geared specifically as a viable alternative to the manual. Most of it due to Roth.
I'm not real familiar with the fill on twinned or multiple Roth tanks. I'm guessing its like a monoflo tee. I'd rather see separate fills and vents if it were mine.
The pickup tubes and the diabolical valve were quickly abandoned in the field due to the float type pickup plastic tubing always broke or the valve wouldn't open.
Hence, the manufacturer override.0 -
It depends on the driver whether or not a spill occurs here. If the driver is experienced and on his game, there would be no spill because he would be listening for two whistles (one on each tank) and when the first whistle stops, he would stop filling.STEVEusaPA said:Are you guys saying with one tank at 3/4 and the other below an 1/8th, that filling these tanks won't cause a spill?
If the vent alarm in the tank 3/4 full is not working and it was not known that this is a twin Roth setup, it would be harder but a conscientious driver would probably hear a gurgling noise and wonder what was up.
By the way, I would advocate for separate fills for Roth tanks.
The picture shows a vent manifold. I know this because the tee is two inches on all sides. If it were a fill manifold, the bull would be smaller. I believe 1/2" id. These cannot be filled slowly; they must be pressure filled at or above 40 gallons per minute or the first tank would get more oil. I've seen delivery instructions that state to fill these slowly; I ignore them per manufacturers instructions. There used to be stickers that were supposed to be placed at the fill box for these but I haven't seen one in a while.0
- 128 Chimneys & Flues