Webstone valves for primary secondary
Snowmelt
Member Posts: 1,425
I saw these valves, I’m the first one to say press is great. Gets me in and out very fast https://www.supplyhouse.com/Webstone-88655-1-1-4-x-1-1-4-Press-Full-Port-Brass-Ball-Valve-w-Reversible-Handle-Primary-Secondary-Loop-Purge-Tee
Spacificle for a condensing boiler in a closet where there is no space I’m going to call the rep on Monday.
Spacificle for a condensing boiler in a closet where there is no space I’m going to call the rep on Monday.
0
Comments
-
2 copper press tees will accomplish the same thing at a fraction of the cost. The only extra labor is cutting and prepping one very short piece of copper pipe.Steve Minnich0
-
Keep in mind putting a valve between two closely spaced tees is like moving the branches 2 feet apart.
A standard ball valve is about 4' of EL, full port maybe 1/2 that. You are adding a bit of pressure drop between closely spaced tees when you put in a valve.
It may, or will induce some flow to the branches. Maybe not enough to cause problems, so make sure the valve is worth the pressure drop.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
My follow up question is would it matter what side the heating loop or the boiler loop is on. Could I go either way, it doesn’t look no worse then what webstone has for navien with the flex in middle of the valves. https://www.supplyhouse.com/Webstone-5FK4-WIF-1-1-4-Sweat-Complete-Near-Boiler-Manifold-Piping-Kit-for-Wall-Hung-Boilers?gclid=EAIaIQobChMIheGbjeC53gIVg5-fCh3zSQ43EAQYASABEgLd5vD_BwE
I kinda like the first product I put up there.0 -
Do you want the boiler in the primary or secondary loop?
I always considered anything that went in and out of the branches to be a secondary load, straight thru the primary flow. The boiler could be in either loop depending on you piping logic.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Those injun-eeeearrrrs I work with always call it an injection loop. They dont recognize the phrase primary/secondary.
I always associate injection as variable speed, but I guess.....Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
I suppose injection would be a fair way to describe it, as long as the closely spaced tees are involved. You only have a P/S piping if two tees are spaced and piped properly. That is the biggest mistake I see, lack of the tees on the same pipe.
These schematics could be considered injection loops with fixed speed circs used.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I've always had trouble deciding what to call it when the boiler and loads are both "secondary" loops off the primary. I like the term Injection Loop, that would eliminate a lot of confusion. Thanks0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements