Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Hartford loop looks high

Options
Hartford loop looks high
Take a look at the pictures please 67 is barely getting water from the return when Vxt is feeding

Comments

  • Steve_210
    Steve_210 Member Posts: 646
    Options
    More
  • Steve_210
    Steve_210 Member Posts: 646
    Options
    M
  • Steve_210
    Steve_210 Member Posts: 646
    Options
    More pics


  • New England SteamWorks
    Options
    Whatever your issue, that Hartford loop isn’t it. It’s not too high , but if it was, it would be a Gifford Loop.
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Fred
    Fred Member Posts: 8,542
    Options
    That's not a correct Hartford loop. The Hartford loop should come up from that copper return that is on the floor (it should be a couple inches below the boiler water line) and that pipe that drops down from the Equalizer should continue into the boiler.
    1MatthiasNeild5delta T
  • Steve_210
    Steve_210 Member Posts: 646
    Options

    Manual
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,215
    Options
    Yep, another backwards Hartford Loop. Here in the Windy City virtually every contractor installs the Hartford Loop too low. I may find 1 in 50 at the right height or above.
    To learn more about this professional, click here to visit their ad in Find A Contractor.