Hartford loop looks high

Hartford loop looks high
Take a look at the pictures please 67 is barely getting water from the return when Vxt is feeding

Comments

  • Steve_210
    Steve_210 Member Posts: 647
    More
  • Steve_210
    Steve_210 Member Posts: 647
    M
  • Steve_210
    Steve_210 Member Posts: 647
    More pics


  • Whatever your issue, that Hartford loop isn’t it. It’s not too high , but if it was, it would be a Gifford Loop.
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Fred
    Fred Member Posts: 8,542
    That's not a correct Hartford loop. The Hartford loop should come up from that copper return that is on the floor (it should be a couple inches below the boiler water line) and that pipe that drops down from the Equalizer should continue into the boiler.
    1MatthiasNeild5delta T
  • Steve_210
    Steve_210 Member Posts: 647

    Manual
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,251
    Yep, another backwards Hartford Loop. Here in the Windy City virtually every contractor installs the Hartford Loop too low. I may find 1 in 50 at the right height or above.