boiler that needs some work

Options
Snowmelt
Snowmelt Member Posts: 1,415
here is a pic of the steam boiler i was chatting about last week. its not doing to good, i think they already replaced the sections. i kinda told them its still not done right. Its at a art school in NJ.

Comments

  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    its a 280,000 btu i think its a 7 section , the book says 3 inch pipe they used 2 inch pipe
  • kcopp
    kcopp Member Posts: 4,432
    Options

    GroundUp1MatthiasCanucker
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Options
    The installer took advantage of “artistic license”—NBC
  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    kcopp, doesn't that warrant a double palm? (with Rikher -sp?)
    kcopp
  • KC_Jones
    KC_Jones Member Posts: 5,739
    Options
    Come on guys it's tough to get it right, it's not like there is a book that comes with the boiler telling you how to pipe it correctly.......
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    kcopp1MatthiasSolid_Fuel_ManCanucker
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,545
    Options
    We all know 2" is the most popular size and why. Over 2" you have to weld it or get out the big die. Since a Ridgid 141 is $1500 you know they are not gonna do that. They can't read the boiler manual but can read the $$ in there bank account. Or they will copper it.

    Not a big fan of Mega Press especially for steam but it would be better than undersized pipe.

    I don't know if MEGA press 2 1/2 and up is out yet but I think it's on the way
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    Yes it’s out and in my 2 local supply houses but I’m going to think there going to be very very expensive.
    I do have a side questions he first riser going up, what size copper do you think that is.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Options
    I wonder if you could get away with those undersized risers...if you upsized a drop header, slowing the steam down, and getting all the water out with a good sized equalizer.
    Such an arrangement might be easier for the customer’s bank account, especially if the header were welded.
    Of course in this case the copper used would make the joints prone to leaking, but 2 inch iron risers to a large drop header might reduce the cost to the starving artists.—NBC
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    I know what you mean NBC . either way it will be big bucks
  • Steamhead
    Steamhead Member Posts: 16,845
    Options

    We all know 2" is the most popular size and why. Over 2" you have to weld it or get out the big die. Since a Ridgid 141 is $1500 you know they are not gonna do that. They can't read the boiler manual but can read the $$ in there bank account. Or they will copper it.

    Not a big fan of Mega Press especially for steam but it would be better than undersized pipe.

    I don't know if MEGA press 2 1/2 and up is out yet but I think it's on the way

    Two words: Precut Nipples.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    KC_Jones1Matthias
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    yes its out , last two boilers i did I used all pre-cut nipples.