Barnes and Jones Big Mouth Installation

Roddy
Roddy Member Posts: 63
I'm thinking of going to Barnes & Jones Big Mouth Main Vents on my single pipe system. I currently have a couple of the smaller Gorton Main Vents on each of my two returns and they are almost touching the ceiling in my basement. Instead of lowering any existing pipes to accommodate the larger Big Mouth Vents, can a do a drop down configuration from the current location / ends using a couple 90 degree elbows to make it easier on myself? Anything wrong with dropping down then coming slightly back up to give me the space I'll need?

Comments

  • KC_Jones
    KC_Jones Member Posts: 5,722
    If you are planning what I think you will create a water trap which is not good.

    It fills with water, steam pushes water into vent cooling it, so it opens and blows steam. Lather rinse repeat.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    1MatthiasRoddy
  • JUGHNE
    JUGHNE Member Posts: 11,042
    Cut and build a pocket box above the vent.
    Or just cut the ceiling open....depends where it is.
    Roddy
  • Sailah
    Sailah Member Posts: 826
    I think creating a loop is a mistake and will cause water to spit. Better to go up as high as possible and let gravity do the hard work.
    Peter Owens
    SteamIQ
    Roddy