Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
steam rad vent - adjustable
Rick T
Member Posts: 16
On a Hoffman 1A adjustable vent, is the fastest setting equal to a non adjustable vent (Hoffman 40), or is it the middle number?
0
Comments
-
A Hoffman 1A vents between .020 and .145, a Hoffman 40 vents at .042. I prefer Ventrite No.1's as the are easier to adjust. It can be difficult to get the screw cap to seat properly in the Hoffman 1A, the knob on the Ventrite just turns so is fool proof.0
-
At setting #4, the Hoffman 1A vents at about the same rate as a #40.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements