Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Dunkirk boilers
meestorapple
Member Posts: 1
I have a Dunkirk D247 hot water boiler. It started firing up for a couple minutes then would shut off for 45 seconds and then fire up again. I turned off the power and when I turned it back on minutes later the electronic spark kept sparking , the pilot was lit but low flame and the boiler would not fire up. Any suggestions would be appreciated
0
Comments
-
First guess would be to clean pilot burner and also clean flame sensor. BTW, don't lose the orifice out of the pilot burner.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements