Dunkirk boilers
meestorapple
Member Posts: 1
I have a Dunkirk D247 hot water boiler. It started firing up for a couple minutes then would shut off for 45 seconds and then fire up again. I turned off the power and when I turned it back on minutes later the electronic spark kept sparking , the pilot was lit but low flame and the boiler would not fire up. Any suggestions would be appreciated
0
Comments
-
First guess would be to clean pilot burner and also clean flame sensor. BTW, don't lose the orifice out of the pilot burner.0