Glycol Calculations
KeenGreen
KeenGreen Member Posts: 27
I am trying to find a simple formula to calculate the amount of glycol in a heating system.
My customer has 3300' of 5/8" oxy tubing, 12' of 2" copper with a number#30 expansion tank.
Glycol will be 50%.
Does anyone have a simple calculator available?
Thanks in advance.
Jeff
    hot_rod Member Posts: 27,472
    What about the boiler capacity, it could be the largest number?
    35-n40% is usually adequate, unless you expect -50 below inside :)
    Glycol doesn't transfer heat as well as water and requires more pumping power, as well a fluid maintenance.
    Select a top brand$$ with good inhibitors and blend to a reasonable protection %.
  • Leonard
    Leonard Member Posts: 903
    edited October 2018
    no idea on tank.
    But just because it's interesting to see the numbers on long tubing .....
    Tubing Volumne = length x cross section area ( using ID)
    1728 cubic inches = 1 cubic foot = ~7.48 gal
    3300' of 5/8" oxy tubing ..... assuming it's 1/2 ID that internal volume is:
    77715 inch^3 = 4.497 ft^3 = 33.6 gallons .
    I don't know oxy tubing.....Measure ID of your tubing.
    If it's 5/8 inch ID then it's 52.5 gal
    12' of 2" copper...... assuming it's 2 inch ID that internal volumne is:
    452 in^3 = 0.26 ft^3 = ~1.96 gallons
    Measure your pipe ID.
    KeenGreen
    EBEBRATT-Ed Member Posts: 20,190
    I get 35.6 gallons of system capacity plus your boiler or heat exchanger. You can find their volume from the manufacturer.
    So far 35.6 x .5=17.8 gallons @50% glycol.
    Their is no calculator it's all math
    KeenGreen
  • GroundUp
    GroundUp Member Posts: 2,513
    My calculator says 44.22 gallons in 3300ft of 5/8" PEX and 1.93 gallons for 12ft of 2" type L. A #30 Amtrol holds about 2.25 gallons. So my total says 48.4 gallons, plus boiler or exchanger. I assume you'll have some other piping, pump, manifolds, etc to figure in as well
    KeenGreen
    Use the commercial sizer program at Amtrol, it allows for glycol %, as that will change tank size.
    amtrol expansion tank sizer