Boiler Drain Cap? Dripping from Drain valve
vaiozh
Member Posts: 4
in Gas Heating
Recently paid to do maintenance on the bolier and notice the drain area continues to drip out water water overfilling the white pan fairly quickly. Before two pipes were dripping, now the long pipe no longer drips but drain valve continues to drip water. Called the heating professional he suggest that it is normal to have some water coming out the drain pipe and it is very common for boiler. He recommend buying a brass cap with washer to put on it. Does that sound reasonable? Do we need to replace the drain valve? Thanks.
0
Comments
-
-
Brass cap w/washer will work.
Repair valve would be better.
Replace would be best.
The long pipe is coming off your relief valve. If that's dripping, you'll need to find out why:
-Air in system.
-Failed/waterlogged expansion tank.
-Water feed not sealing properly.
Just to name a few.
NEVER cap off the pipe from the relief valve.There was an error rendering this rich post.
2 -
Is that fairly expensive to replace or repair?0
-
@STEVEusaPA, the dripping now is not from the relief valve (long pipe) that seems to stopped, the dripping seems to continue from the boiler drain and it has been slow down a bit.0
-
I would go for the brass cap on the boiler drain. To replace the drain valve, the boiler and perhaps the entire system would have to be drained down.
If there are isolation valves between the boiler and the system piping then only the boiler would have to be drained.
This is probably why the maint person did not want to change it. Bleeding air out of the system may take some time.
Most people in the business carry the brass caps on their truck just for this purpose.
The cap also may prevent someone from getting a bucket of water out of the boiler for whatever purpose.
You should be able to lift the lever on the pressure relief valve and it should pass water and then reseat.
Your pro should have done that.
You want to run a gallon or two thru it to flush it out and let it snap shut......a half second lift will not flush it well enough and may introduce a drip. Your auto fill valve should replace the water
To replace that may require the same drain down of the system.1 -
@vaiozh, the brass cap and hose washer are fine for now. Sooner or later you will have to change another part on the boiler that requires draining the system. You can wait and do the rain valve then.
Put a tag on the boiler to replace the drain valve so you and the service company won't forget.
check the water pressure in the boiler. Should be 15-20 psi depending on the water temperature. Over pressure will cause the relief valve .....long pipe to leak0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements