Best set up for air heat exchanger
cnmdesign
Member Posts: 103
I saw this was covered before, but there was no conclusion that fit my needs.
Given:
The fan spects:
Axial fan Motor
YWF4E-250B-2T
120v 60Hz 0.58A 70w 1580 r/min
120v 60Hz 0.32A 40W 1310 r/min
7uf/450V CLF
on a 50K water to air heat exchanger.
https://chillxchillers.com/air-to-water-heat-exchangers/zephaire-2-speed-air-to-water-heat-exchangers?sku=ZAU0120500ZA-2&gclid=EAIaIQobChMIvs-b_PPJ3AIVA5ppCh2CuQ_KEAkYASABEgIrNvD_BwE
on a 3/4 pex x 6' run.
Should I run the water through a Caleffi Quick Setter to make sure of GPMs, or will this throw off the other zones?
1500 sq/ft walk out basement, just over half under ground with one 6' slider.
Would staying with 1" loop be worth buying a 50 ft coil of pex for just 12 ft?
3/4 at 4 GPM will only get me 40K.
This unit will be on it's own zone.
What would be the optimen set up for this unit?
Need G PMs, type and location of T-stat.
Will it heat the basement well enough to shut off for awhile?
Thanks
Given:
The fan spects:
Axial fan Motor
YWF4E-250B-2T
120v 60Hz 0.58A 70w 1580 r/min
120v 60Hz 0.32A 40W 1310 r/min
7uf/450V CLF
on a 50K water to air heat exchanger.
https://chillxchillers.com/air-to-water-heat-exchangers/zephaire-2-speed-air-to-water-heat-exchangers?sku=ZAU0120500ZA-2&gclid=EAIaIQobChMIvs-b_PPJ3AIVA5ppCh2CuQ_KEAkYASABEgIrNvD_BwE
on a 3/4 pex x 6' run.
Should I run the water through a Caleffi Quick Setter to make sure of GPMs, or will this throw off the other zones?
1500 sq/ft walk out basement, just over half under ground with one 6' slider.
Would staying with 1" loop be worth buying a 50 ft coil of pex for just 12 ft?
3/4 at 4 GPM will only get me 40K.
This unit will be on it's own zone.
What would be the optimen set up for this unit?
Need G PMs, type and location of T-stat.
Will it heat the basement well enough to shut off for awhile?
Thanks
Combat Veteran owned, Final Salute LLC on FaceBook & Twitter.
www.afinalsalute.com
www.afinalsalute.com
0
Comments
-
-
Up stairs is just under 37K. Can't see the closed in basement being a greater loss. Heat loss from old 90K CI kept the basement around 50* even on a design day with open floor joist and block walls.hot rod said:What is the calculated heat load for the basement? The coil, pipe, gpm, etc all get sized to the actual load.
New one will not add that much heat to the room. Only what comes off the P/S pipes. Not looking for 70*. This was a last minuet add on. Was not going to heat this winter with boiler. Have small gas stand alone for cold cold days and nights.
Not saying there is none but even on the calculators I used for the up stairs, there was no place to do a basement.
30x50 room. Fan is located in the walk out end with the slider. Got the exchanger for free. Going with it. Just want to know how to max it out. If the out put is to hot, how would I choke it back?
ThanksCombat Veteran owned, Final Salute LLC on FaceBook & Twitter.
www.afinalsalute.com0 -
Is this a pumped zone all by itself? If so a multi speed circulator will give you a bit of adjustment. The B&G Vario has a 9 position selector, nice for fine tuning.
A Quicksetter would allow you to see and confirm GPM if that is important. Sounds like a very small load if boiler standby losses kept it 50F?
3/4" should be plenty tube size.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream-1 -
4 Caleffi zone valves with an Alpha2. Up stairs on one, one DHW, one for the (exchanger) basement and one on stand by for new out building later.hot rod said:Is this a pumped zone all by itself? If so a multi speed circulator will give you a bit of adjustment. The B&G Vario has a 9 position selector, nice for fine tuning.
A Quicksetter would allow you to see and confirm GPM if that is important. Sounds like a very small load if boiler standby losses kept it 50F?
3/4" should be plenty tube size.
Hope this helps, so, what would you suggest for a set up?
Will the 3/4 max 40K be enough to get over say 60 or 65?. What GPM should I run? Is 4 OK? That should max out the 3/4 pex. If no QS how will I know what the flow rate is?
ThanksCombat Veteran owned, Final Salute LLC on FaceBook & Twitter.
www.afinalsalute.com0 -
I'd be surprised if that basement load would be much more than 30- 35K, 4 gpm should be more than adequate. The basement will be a lower load than upstairs if it is mostly below ground and has hasted space above.
The thermostat will shut down the unit to prevent over heating the space. if the unit and flow rate is oversized by a bit, it just turns off sooner.
You could install a QS to balance and observe, but without an exact load number, what would you balance it to?
Additionally if you are not concerned about maintaining 70F, the load is even lower.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream-1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements