Connecting my header to the Main
![rwilson2526](https://secure.gravatar.com/avatar/c48fac6174c79c144ad1d8150aa2b402/?default=https%3A%2F%2Fvanillicon.com%2Fe54cbdca4770e0c5e1ae3462b0080736_200.png&rating=g&size=200)
rwilson2526
Member Posts: 16
Hi Guys,
I was on here last year when I realized my H/E was shot. I decided to replace the heat exchanger and repipe the whole mess. Coming down the home stretch. First thing, lets get it out of the way, I know I should have done a drop header!
That being said I now have to connect my 2" Tee off my header to my 3" main. I don't have the dimensions in front of me but but the offset is just a bit too far to connect with 2 - 45's
Question is which is better? should I just connect them with 2 90's or should I use 4 - 90's and do a swing joint and put the maximum pitch on the pipe? I will have a lot of condensate coming back down as several of my radiators take off before my dry returns but I was wondering if the extra turns is a bad thing.
And ignore those long nipples coming out of the tops of the returns for the vents. I am installing 90's to switch them back and follow the pitch of the returns. (learned that here too!)![](https://us.v-cdn.net/5021738/uploads/editor/rj/94tm5f4jhkyg.jpg)
Thanks
I was on here last year when I realized my H/E was shot. I decided to replace the heat exchanger and repipe the whole mess. Coming down the home stretch. First thing, lets get it out of the way, I know I should have done a drop header!
That being said I now have to connect my 2" Tee off my header to my 3" main. I don't have the dimensions in front of me but but the offset is just a bit too far to connect with 2 - 45's
Question is which is better? should I just connect them with 2 90's or should I use 4 - 90's and do a swing joint and put the maximum pitch on the pipe? I will have a lot of condensate coming back down as several of my radiators take off before my dry returns but I was wondering if the extra turns is a bad thing.
And ignore those long nipples coming out of the tops of the returns for the vents. I am installing 90's to switch them back and follow the pitch of the returns. (learned that here too!)
![](https://us.v-cdn.net/5021738/uploads/editor/rj/94tm5f4jhkyg.jpg)
Thanks
0
Comments
-
Looks like 2-inch pipe. I hope you didn't reduce the size of the boiler's steam outlet................All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Nope, 2" tap. Basically fabricated crowns near boiler piping sketch exactly.0
-
-
Thanks for the information. That's the route I will go. This leads me to my next question. In trying to eliminate all copper in this new repipe, the last piece is this 3-2 adapter screwed into my 3" T on the main. On a side note, I know that a T in the center of a main is not ideal but I figured the dead men don't make mistakes and I'm not up for splitting it into 2 right now. Even with my terrible previous installation the house always heated evenly.
Anyway, how would you go about getting this thing out of the T. I was going to cut it flush and then try to split it inside with hack saw blade and chisel. Then I was wondering if that is a screwed on fitting over a nipple and maybe I'll just try to split the fitting on the outside exposing the existing nipple. At least I think that is a nipple in there. Of course we have cold weather coming end of this week so I am tempted to not mess with it at all and sweat a 2" male adapter on it and call it day. Assuming time is not an issue, what's your preference?
0 -
That is a DWV (drain waste and vent) male threaded adapter soldered to a dwv reducing coupling. I would cut it off leaving about 1/4" sticking out of the tee, slice into it very carefully going in almost to the female threads, but not quite all the way, and take a hammer and chisel and collapse the copper inwards to remove, should come out easy.
I assume you have tried to take it out with a wrench? kind of surprised it won't go...0 -
Thanks for the ID. I tried unscrewing with a 2' pipe wrench with 3' length of pipe on the end. Problem is because its horizontal, 7' off the ground and no wall nearby to have something to push off of I can't get it to budge. I had the same issue with one ofthe connections to the dry returns fortunately the black pipe to black pipe connection further back let go. Even after I gotit down and put it in a pipe vice I couldn't get it undone.0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements