Why The Close Tee's
winesalot
Member Posts: 32
I've been doing a bunch of reading on radiant systems with primary and secondary loops. In nearly every discussion or example it comes up that the secondary supply and return lines from the primary loop should be close together. Most say within 4x the primary pipe size? Some also say the primary piping should be straight for 8x the primary pipe size on either side of the pair of Tee's. It's not a problem to comply with these instructions but I'd love to hear the physics of why this matters.
0
Comments
-
A long and short answer.
https://www.caleffi.com/sites/default/files/file/idronics_15_na.pdfBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It has to do with the restriction that develops through the length of the pipe: more as it gets longer. You want the water to "want" to move straight through the pipe and tees (called the *run* of the tee) and not be influenced to move through the tees' branches (called the *bull* of the tee). The longer the pipe between the tees, the more likely water will be influenced to gravitate through the branches.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Thanks for the great answers.
Why is my favorite question. If you don’t understand why then you don’t understand.0 -
Another way to put it - the closer the tees in the primary loop, the less pressure drop between the tees, the less pressure drop between the tees, the less chance of inducing flow in the secondary loops.Steve Minnich0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements