drop header basic question
Options
Snowmelt
Member Posts: 1,415
just a basic question, when building a drop header , is going higher better off the boiler for example, is I can install a 2-1/2 foot riser or a 3 foot riser am I better off with a 3 foot?
0
Comments
-
The higher the riser, the better as far as water dropping out of the steam. If you are using both risers, there probably isn't much difference in being 6" higher.0
-
book only calls for one riser 2 1/2 inch i am going to put it 30 inch high.0
-
Use both risers, always, and don’t bush them down. My opinion of course.0
-
The manufacturers minimum requirements will work . To me the longer the risers the better. If the risers are long enough a regular header is ok. I feel a drop header is more important with short risers. That's just my opinion.
Regardless of what the mfg says I always check the steam velocity of the risers. To me that's the most important thing0 -
Thanks guys, I went to the job to look at the new steam boiler, it’s wider then the old one, that is going to make it a little tougher because it has to be that much tighter.0
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements