just a basic question, when building a drop header , is going higher better off the boiler for example, is I can install a 2-1/2 foot riser or a 3 foot riser am I better off with a 3 foot?

Comments

  • Fred
    Fred Member Posts: 8,542
    The higher the riser, the better as far as water dropping out of the steam. If you are using both risers, there probably isn't much difference in being 6" higher.
  • Snowmelt
    Snowmelt Member Posts: 1,425
    book only calls for one riser 2 1/2 inch i am going to put it 30 inch high.
  • Danny Scully
    Danny Scully Member Posts: 1,440
    Use both risers, always, and don’t bush them down. My opinion of course.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,470
    The manufacturers minimum requirements will work . To me the longer the risers the better. If the risers are long enough a regular header is ok. I feel a drop header is more important with short risers. That's just my opinion.

    Regardless of what the mfg says I always check the steam velocity of the risers. To me that's the most important thing
  • Snowmelt
    Snowmelt Member Posts: 1,425
    Thanks guys, I went to the job to look at the new steam boiler, it’s wider then the old one, that is going to make it a little tougher because it has to be that much tighter.