steam trap repair option - cage units

josephcjosephc Member Posts: 17
I am refurbishing my existing MILVACO H100 traps and looking at Barnes and Jones tables have the option of replacing the guts with a cage unit using the existing cover versus using a cage unit requiring a new cover. The difference in cage unit appears to be spring. I have been advised to use the new cover/cage unit combination. Has anyone experienced installation with existing covers vs new covers and found one better experience over the other? Does the B&J cover combo go in easier than trying to use an old cover? is it hard to hold the cage unit in place using the existing cover?

Comments

  • RayWohlfarthRayWohlfarth Member Posts: 430
    I have done it both ways and had no issues with reusing the existing covers. We replaced 80 of them in one apartment building and reused every cover. Didnt have one failure and its been 6 years. Customer told me this apartment has the lowest costs per square foot of any of his buildings. So far so good.
    Ray Wohlfarth
    Boiler Lessons
    Click here to take Ray's class.
    Click here to buy Ray's books.
  • gerry gillgerry gill Member Posts: 2,795
    As long as the cover can hold the cage unit in position, go for it.
    gwgillplumbingandheating.com

    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • SailahSailah Member Posts: 658
    The reason for new covers is simply a height issue. Many steam traps originally came with discs which are lower in height like a Mepco 1E. All cage units are basically the same height so in order to fit them in with a spring that will hold the gasket tight, a new cover is sometimes required.

    Other things that can factor: If you can't get the old seat out, often that will raise the cage unit up and a new cover may be required.

    But I would suggest using original covers whenever possible. You know they fit, they are original and it's cheaper. Sometimes building owners would buy new covers just so that they could visually inspect that the work was actually being done by outside contractors.

    Peter

    Barnes & Jones emeritus
    Peter Owens
    SteamIQ
  • josephcjosephc Member Posts: 17
    These are the MILVACO traps that will be updated. They are pretty squat so would this be a case for the new cover to give more room for cage unit?
  • SailahSailah Member Posts: 658
    Just by looking at it, yes I'd say you need new covers. And only reason for that is height for cage units. Pretty simple to repair, remove cover (I only use an impact gun to do this now), remove seat if present. Drop in new cage unit, screw down cover.
    Peter Owens
    SteamIQ
  • josephcjosephc Member Posts: 17
    The Barnes and Jones chart for the cage unit (2164) for my traps has the words "seat in" in notes column. Does that mean I leave the existing seat alone and install the cage unit on top of it?
  • SteamheadSteamhead Member Posts: 12,115
    That is correct.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
Sign In or Register to comment.

Welcome

It looks like you're new here. If you want to get involved, click one of these buttons!