Pros cons to spiro/exp location
Adkworker
Member Posts: 3
in Oil Heating
Upgrading a system with new components all 5 zones with taco sentry valves. Zone loop has 007 and boiler loop has 007. Biasi low mass fired at 125k. Reason for p/s is due to a pellet boiler being installed in parallel next to boiler with 3way valves. Does anyone see an issue, this location suits the extisting layout best for me.
0
Comments
-
Does the design requirements call for 007's?
There was an error rendering this rich post.
0 -
Have 10 ft of hp on secondary loop so a 006 can’t cut it per the curve. Don’t want a smaller circbon boiler loop want to at least keep them the same. Plus the 007 will cover the extra hp when using the second boiler. Adds another 30ft of 1” tubing and some fittings0
-
maybe include a drawing of what you propose. Air purgers do their best work at the hottest point in the system, right at the boiler supply if possible.
The expansion tank need not be installed at the purger, it needs to be located so all the circulators are pumping away from the tank connection.
It's fine to have a circulator at the boiler return, as long as the tank connection is correct.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
this is where the spirovent goes
"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0 -
-
Where are the two boilers connecting?
A hydraulic separator can clean up some piping detail and provide 4 important functions.
You mentioned 3 way valves? for boiler return protection?
If so here is a good example of parallel boilers, 3 way protection, air, dirt, magnetic and hydraulic separation provided by one product.
It places all the components in the best location for multiple functions. Air removal at the hottest point, expansion tank ideally located, hydraulic separation for boilers and distribution, and a magnetic function should you choose ECM circulators now or in the future.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements