Home AC Compressor High-Side Pressure Cycling
GarrettB
Member Posts: 1
My 7 yr old 2.5 ton Goodman AC unit is now working OK (the thermostat failed!), but the svc tech noted that the high-side pressure slowly cycles from 380--580 psi (~every 10 seconds), and the amp draw there is in synch with that at 8.5--12 amps. Any idea what to look for???? It DOES work, but that pressure over the nominal 450psi is troubling. --gdb
0
Comments
-
If the condenser fan is running normally then the condenser coil probably needs cleaning. Spray coil cleaner on it and flush with water. Follow the directions on the coil cleaner and folly good safety practices. Power off, rubber gloves face protection.
About the only other reason would be if the unit was overcharged1 -
I learned on my first 410A job how easy it is to overcharge those, especially if microcoil.0
-
Ed, I can see how the pressure would be up from plugged coil or overcharge......but how does it drop and then rise again?
(assuming the unit stays running)
Could be TXV searching??0 -
Normal 450? 450 even sounds excessive
Non condensibles, txv probe in wrong spot, oversized txv, overcharge will cause such issues.
What model units both indoor and outdoor? Txv or piston?
What was the suction side doing? What's the superheat and subcooling?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Has anyone checked the pressures since the original install?
Could this have been going on since day one?
I see ChrisJ's point on the non condensibles (air) in there that may run the pressure up and down.
The tech should have noticed the plugged coil if so.0 -
Heat pump or straight A/C? Mod # please,0
-
Non-condensable gases, overcharge, restriction depending on what suction pressure is doing, underperforming fan (1 or 2 speed?), dirty coil (some coils are two layered), air obstruction surrounding the unit.Steve Minnich0
-
I'm going with failed expansion valve after reading the symptoms in the OP. I got volunteered for a favor on one of these and saw the exact same as described. The good news is that if you go back with an OEM valve the connections are all mechanical ( Rotolock type from memory ).hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements