Aquastat for hot water storage tank

DonnR
DonnR Member Posts: 2
I have an NG on demand water heater with a electric water heater utilized as a storage tank, I am currently using the lower tstat to control the circ pump, the tstat is not reliable, and I would like to replace it with an aquastat. The probe will be going into a 3" well, and I would like the aquastat to turn the circ pump on at 115 degrees and off at 125 degrees.
Any suggestions?

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,019
    Honeywell L4006A with adj differential

    There was an error rendering this rich post.

    HVACNUT
  • HVACNUT
    HVACNUT Member Posts: 6,330
    I dont know the model#, but the clamp on version of the L4006A. Where are you planning to put a well on an electric water heater?
  • DonnR
    DonnR Member Posts: 2
    I am going to take out the bottom element, bush it down and install the well there.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,019
    Good idea .... The 4006

    There was an error rendering this rich post.