Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

2 pipe steam

Snowmelt
Snowmelt Member Posts: 1,425
a few questions, on 2 pipe steam the customer wants to replace 3 rads that are kind of in the way (which they are) and swap them out with sun rads that are in the wall to gain some space is this something that can be done, I think so but just asking, I would like to see a picture of a recess rad with the steam trap and shut off valve.

Comments

  • Steamhead
    Steamhead Member Posts: 17,387
    If there's room in the bottom of the Sunrad, you can put the trap and valve there. Otherwise, they can go in the basement under the rad.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    GBart
  • Snowmelt
    Snowmelt Member Posts: 1,425
    Thanks steam head, will moving the rads a few feet over would that mess the overall steam getting to the radiators, which brings me to my next question, I looked at the boiler piping what bothered me was the supplies on top of the peerless boiler just went up to the main run, i will take pics in a few days,
  • Steamhead
    Steamhead Member Posts: 17,387
    As long as they are pitched properly, and you don't reduce the pipe sizes, you should be OK.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Snowmelt
    Snowmelt Member Posts: 1,425
    OK thanks,
  • GBart
    GBart Member Posts: 746
    Aye and make sure all pipes are insulated.