Honeywell T8775 non-programmable thermostat and Taco Viridian circulators?

jwalk
Member Posts: 1
I'm trying to install a Honeywell T8775 heat-only non-programmable thermostat. I believe I need to use the included resistor because we have 2 different zones with Taco controllers, but they aren't the typical zone valves that Honeywell describes in their install manual. We have 2 Taco Viridian Circulators (#VR1816-HY1-FC2A00) connected to a zone relay. I'm not exactly sure where to place this resistor.
Here are a few photos of the equipment:



Here are a few photos of the equipment:



0
Comments
-
I think the resistors are to shed away stray voltage when power stealing thermostats are used with just two wires?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
the resistors are for zone valves with powered t stats, dont need the resistor with that zone panel, just change the t stat"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
Categories
- 120.3K All Categories
- 83.6K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 414 Carbon Monoxide Awareness
- 30 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.6K Gas Heating
- 114 Geothermal
- 152 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 736 Plumbing
- 5.2K Radiant Heating
- 357 Solar
- 13.8K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 36 Industry Classes
- 70 Job Opportunities
- 14 Recall Announcements