Honeywell T8775 non-programmable thermostat and Taco Viridian circulators?
jwalk
Member Posts: 1
I'm trying to install a Honeywell T8775 heat-only non-programmable thermostat. I believe I need to use the included resistor because we have 2 different zones with Taco controllers, but they aren't the typical zone valves that Honeywell describes in their install manual. We have 2 Taco Viridian Circulators (#VR1816-HY1-FC2A00) connected to a zone relay. I'm not exactly sure where to place this resistor.
Here are a few photos of the equipment:
Here are a few photos of the equipment:
0
Comments
-
I think the resistors are to shed away stray voltage when power stealing thermostats are used with just two wires?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
the resistors are for zone valves with powered t stats, dont need the resistor with that zone panel, just change the t stat"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements