Buderus G115 stinking up my basement
Gary_on_21117
Member Posts: 1
So I just moved into a home with the G115 and everytime it fires up I can smell burnt fuel oil. Turns out someone had put a Beckett burner on it that was never spec'd for the unit, so I luckily was given an home warranty when I purchased the home and was able to get the correct burner installed at no cost (was shocked). I still smelled the smoke after the install but gave it a couple days to burn off any oil or whatever from the installation and it is still sending a little exhaust in the room on every start.
A little about my exhaust tubing: It was piped into a brick chimney and had the smell, I took down the chimney and installed all new flue pipe in the basement with one 5 foot length of flue at about a 40-50 degree angle then straight up with all-fuel Duratech maybe 18 feet, still had the same smell, I taped everything, still smelly. I don't believe it's the exhaust tubing, nor did any of the oil techs that have been out.
Anyone have any ideas as to what is happening here? Thank you in advance.
A little about my exhaust tubing: It was piped into a brick chimney and had the smell, I took down the chimney and installed all new flue pipe in the basement with one 5 foot length of flue at about a 40-50 degree angle then straight up with all-fuel Duratech maybe 18 feet, still had the same smell, I taped everything, still smelly. I don't believe it's the exhaust tubing, nor did any of the oil techs that have been out.
Anyone have any ideas as to what is happening here? Thank you in advance.
0
Comments
-
Isn't this a G115WS direct vent boiler and you're trying to fire it into the chimney?
You need a competent professional to go over the whole system. Clean the boiler, check your chimney/flue pipe, and set the burner up with the right nozzle, draft, smoke, combustion air, etc.
Also, is there enough combustion air when the burner runs?
Is there a nice new high efficiency dryer sucking all the air out of the room?
There was an error rendering this rich post.
3 -
Agreed, you need a Buderus trained technician.
Do you have a CO detector or alarm?
I saw a Buderus put out 30,000ppm CO because the baffles were installed wrong.0 -
That boiler and burner need to be set up to the manufacturers specifications, with proper combustion analysis performed. And it sounds like it will need a lot of cleaning!
Please don't tape the flue pipe.0 -
from manual-- Sealing of the Vent Piping:
The discharge side of the sealed combustion venting system operates under a slight positive pressure. It is
of vital importance to seal all flue joints and screw penetrations to prevent leakage of flue gases into the
building. Pipe joints and other possible flue gas leakpaths should be sealed with high temperature silicone
(500 ºF rated silicone, G.E. 106 or equivalent), or high temperature tape (360 ºF rated aluminum foil tape,
VentureTape 3520CW or equivalent) as necessary.
The venting system shall not be pierced under any circumstance after initial installation.
Combustion measurements shall be performed at the exhaust termination and/or overfire. The breeching
can be pierced for testing as long as the hole is sealed airtight with a bolt, washers and high temperature
silicone.
starts on page 3
amazing things, these manuals
https://www.bosch-climate.us/files/201208201508230.115SCIM_G115_Installation Manual_en_12-2006.pdf0 -
you stated--- " I don't believe it's the exhaust tubing, nor did any of the oil techs that have been out."
how many tech's exactly?, did any refer to the manufacturers manual??
did any check for CO ??0 -
Is there adequate combustion air? Is it the Beckett NX?
Shouldn't be too hard to figure out.
Amazing things, these analyzers.0 -
It doesn't hold up, several manufacturers are now saying to seal it with hi temp silicone, Buderus states that or hi temp tape but I haven't seen a tape hold up for years, silicone holds up.0
-
Both Beckett NX and AFG are approved with G115 so that isn't your problem. Need someone with a combustion analyzer and who knows how to use itTo learn more about this professional, click here to visit their ad in Find A Contractor.0
-
Gbart the manual you listed is for a direct vent boiler. Being this is chimney vented it will be negative at breach and for that reason taping/sealing should not be necessary.. It sounds like a setup issue. Does it do it every time it runs? Does it do it when it shuts down? Does it rumble when it starts? Have they done the filter at the tank?0
-
Check the door gasket.
Rick0 -
This content has been removed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements