Expansion tank location
High pressure drop boilers prefer you pump into them as shown in installation manual suggested piping methods.
Critical on both is the air separator at the hottest point in the system.
The expansion tank need not be at the air separation device.
trainer for Caleffi NA
Living the hydronic dream
Comments
-
I agree as long as on the "high resistance boiler" the pump doesn't have enough head to open the relief valve. If hooked up pri/sec it wouldn't be an issue0
-
Hello Bob,
Would you mind also uploading a diagram of a steel compression tank system with the Airtrol valve as well for everyone? This way they can compare them and understand how the steel compression tank was used first in "pressurized" hydronic heating systems.
0 -
Have you ever seen an expansion tank tied to the system at two points? This is a direct return layout with 2.5" supply and returns.
The system return for the main part of the house has a PONPC and the system return for the rear part of the house has a PONPC. These points are within 2 feet of each other directly above the boiler. The returns combine immediately after the PONPC just ahead of the circulator and then to the boiler so it is pumping away. Not seen in the pic is the system feed and pressure regulator where the expansion tank threads in.
0 -
Yeah, you really don't want two different expansion tank tie- in, in different locations.
Basically you create two PONPC, as such the pressure in various places around the circuit could cause issues like sub-atmospheric conditions allowing air vents to suck instead of blow
If in fact they tie into the same pipe within a few feet of one another it probably will not cause issues. Are they pre-caherged to the same pressure?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Here you go. And a a copy of the Amtrol Handbook to learn a lot about expansion tanks types and applications.leonz said:Hello Bob,
Would you mind also uploading a diagram of a steel compression tank system with the Airtrol valve as well for everyone? This way they can compare them and understand how the steel compression tank was used first in "pressurized" hydronic heating systems.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Only one expansion tank. Years ago it was a steel tank with no bladder and the system fill was 20' away. The fill and pressure regulator were moved to the neck of the new bladder type expansion tank when the modcon was installed. https://i.imgur.com/ad5hyFh.jpghot rod said:Yeah, you really don't want two different expansion tank tie- in, in different locations.
Basically you create two PONPC, as such the pressure in various places around the circuit could cause issues like sub-atmospheric conditions allowing air vents to suck instead of blow
If in fact they tie into the same pipe within a few feet of one another it probably will not cause issues. Are they pre-caherged to the same pressure?
0 -
You need to get that fixed.0
-
With two points of tie you will create an unwanted bridge for flow if there is any pressure difference at the pickup points.0
-
I get it now, single tank tied into two places.flat_twin said:
Only one expansion tank. Years ago it was a steel tank with no bladder and the system fill was 20' away. The fill and pressure regulator were moved to the neck of the new bladder type expansion tank when the modcon was installed. https://i.imgur.com/ad5hyFh.jpghot rod said:Yeah, you really don't want two different expansion tank tie- in, in different locations.
Basically you create two PONPC, as such the pressure in various places around the circuit could cause issues like sub-atmospheric conditions allowing air vents to suck instead of blow
If in fact they tie into the same pipe within a few feet of one another it probably will not cause issues. Are they pre-caherged to the same pressure?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements