AO Smith Water Heater
Harvey Ramer
Member Posts: 2,261
Just this week I installed a new Cyclone MXI 199 water heater. I turned it on and it ran for 5 minutes and then shut down on an error and said the flame sensor was shorted out. I dickered with it for a little bit, then I pulled the flame sensor. It is a straight rod about 4" long. I noticed that the rod did not appear to be 100% aligned with the porcelain and the bracket. I laid it on a straight edge and straightened out the rod. It has run fine ever since.
Thoughts? Was it bent from the factory or did the rod warp from the heat? AO Smith says there are only 2 things that cause this error; water in the combustion chamber or cracked porcelain. Maybe we just found a third cause?
Thoughts? Was it bent from the factory or did the rod warp from the heat? AO Smith says there are only 2 things that cause this error; water in the combustion chamber or cracked porcelain. Maybe we just found a third cause?
0
Comments
-
sounds like the sensor was bad from the manufacturer. Who ever put it into the water heater heat missed that it was bent....0
-
@kcopp , or most likely didn't care.
@Harvey Ramer
Surprised they didn't tell you "we have never seen that problem before" or "all our equipment is factory tested" or "that just can't happen"1 -
Lest we forget JohnNY's disaster Cyclone from a couple years ago .
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
That thread is here:Rich said:Lest we forget JohnNY's disaster Cyclone from a couple years ago .
https://forum.heatinghelp.com/discussion/154183/a-o-smith-water-heater-big-problems-no-help-johnny-updated-3-27-15-11-30am/p1
It speaks for itself.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I well remember that thread. I looked at HTP but none of the Phoenix models met the demand. Most of them are capped at 160° degrees and the sanitizer model, which meets the required 180° temp, only has a 50 gallon tank. That's not enough to meet the requirement of 175 gallons of 180° water in the first 45 min.
Ruud has a new Triton that may have the capacity. I haven't looked at them that much yet.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements