pipes banging and water coming out of vents

Snowmelt
Snowmelt Member Posts: 1,428
went to a service call this morning , home is under construction , there where three rads moved. one was banging and water came out of the vent. I see it was moved from one location to another, there was a slight pitch going the wrong way and the rad was perfectly level. I pitched the rad and bang stopped a little other rad had a lot of water coming out of rad but that was level also. I pitched the rad to go back towards the boiler , it slowed down the water, no banging came from the rad. the air vents looked old and original, could they just be bad from time. near boiler piping was done at a minimum but still looked good, sight glass was NOT jumping but a little dirty. third rad was working just fine. my question is , if the rad is dead even with no pitch would it still bang.

Comments

  • Danny Scully
    Danny Scully Member Posts: 1,452
    Well you pitched both rads and stopped the banging correct? So you answered your own question :wink: How big of a level did you use to confirm? Really you need a torpedo level to check section by section. What I’m getting at is that maybe the rad wasn’t in fact level the entire way across. The only rads I leave dead level are recessed cast iron radiators, because if you pitch them (on a one pipe system) you’re actually back pitching the supply. And yes, the vents could just be bad at this point. They have a lifespan and eventually require replacement.
  • the_donut
    the_donut Member Posts: 374
    Pressure issues? Changing vent won't hurt but my experience is water is from obstructed valve. Was valve closed?
  • Fred
    Fred Member Posts: 8,542
    Check system pressure and make sure it is set correctly and that the pigtail isn't clogged.
    Also make sure the supply pipe is sized correctly for the radiator(s).
  • Snowmelt
    Snowmelt Member Posts: 1,428
    Thanks for listening, I was called to the job by a plumber who only likes to do rough ins. I pretty much told him every thing but the make sure pigtail is clean and pressure is corrrect. I will go there at the end of week to see if he fixed the pitches.