Heat dump zone for OWB
Right now my dump zone is tied into it's own loop with a water/air heat exchanger and fan. I'm wanting to tie it into my current garage heating loop and do away with the other WAHX setup. The dump zone will only be used in the case if over load the firebox and my hot water storage tanks won't take anymore or at least won't take the BTUs fast enough to cool the boiler. I'm trying to avoid my boiler going into idle.
My boiler will be heating storage tanks which I draw from for my heat loads. It heats the tanks via a plate heat exchanger. The storage tanks are in my garage as the boiler is in a shed just outside. The FPHX is also in the boiler shed. So from plate HX to storage tank it runs underground.
I've drawn up a plan I'd like feedback on, good or bad, to see if you guys think this will work. Anything i should change let me know. My thinking is if the dump zone needs to come on it will open the diverter valve to the dump side. This will send water up into my current garage heating loop. When the dump is activated it will also switch on my current garage loop circulator to help with the added head of the garage loop. Thought being the pumps would be in series so it should be ok?
Let me know what you guys think.
I would think you'd still want to circulate through storage while in dump mode. Could you add a circulator instead of a diverter valve in that location. Basically have everything all piped into the supply header and the return header.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
@Solid_Fuel_Man thanks for the reply. my thinking was the over heated water would circulate directly through the garage loop. If the dump is needed it's because the storage isn't taking any more heat from the boiler or at least not fast enough. The boiler is only plumbed to a FPHX which has the storage plumbed to the other side. So the storage tank gets heated before anything else.
What if I take out the diverter and just put a tee there with a N/C zone valve on the vertical line that opens if the dump is needed? Then some flow would also go to the storage.
Or would i basically achieve the same thing by just using the temp controller to switch on the garage heating loop. With where the header connections are on both the supply and return headers it would draw in most of the FPHX water and return it to where the circ pulling for the FPHX is drawing from.
The 2 pictures are of my storage tank headers.
The first picture is the supply header. The connecting nearest the wall wall and on the bottom is the FPHX return. And the center connection is the garage loop supply.
The second picture is my return header. The connection nearest the wall and vertical is my FPHX supply. And the last connection that's horizontally is my garage loop return.0 -
My first question would be why the need for a dump? Is this a batch burn type scenario with no damping on the boiler? I'm having trouble understanding your expectations from the system. The tank pictured does not appear to be of much volume, a batch burn does not work well unless there is a HUGE amount of stored energy- like several thousand gallons for a 24 hour batch with an average home. I can understand the want for avoiding idle time, but a damper to send the boiler to idle is a much safer bet than a wild fire and wasted heat via the dump IMO.0
I run batch burns in my boiler. My storage tank is actually 3) 250 gallon tanks stacked. Typically I judge the wood load good enough the fire dies before anything over heats. But if the wood load is too much the boiler goes into idle. I'm wanting to start dumping heat at 190°. If the storage tanks are getting close to boiler temps and there is still a fire going, albeit small fire either way at this point, I would rather dump the heat to a building then send it up the smoke pipe.
With my new plumbing and FPHX I'm putting in I don't think the heat dump zone will be used but I want the insurance if it is needed. One of those rather have it and not need it than need it and not have it things. Thats all.
Attached is a pic of the tank stack0 -
Understood. After some thought, I'm thinking you could benefit from swapping your drawn diverter to a tee, and moving said diverter up to the tee location between the check and garage circ so you are not drawing from storage while in dump mode. Also, I see that you have drawn bidirectional flow in your supply and return headers. In this fashion, during any call for heat you will likely be drawing through your underground/FPHX and bypassing the storage tank altogether. To make storage work in this fashion, I believe we need 4 ports to the tank itself. Counterflow in a header is bad juju0
The design of the diverter tee only allows flow in the center bottom port and out one side or the other. I think to locate it on the garage circ line I would need a zone valve on the vertical dump line and on the garage supply line. The One on the garage would be open and other closed on the dump liner during normal operation then switched during heat dump. which if this did the trick I'm ok with that.
My thinking in the header design using 3" headers with 1" connections was, the larger header would slow the velocity of the incoming and outgoing water and a slight mix of both storage water and FPHX water would be picked up as heat load supply. But this would only happen during boiler firing. I've been running the headers with supply and return this way for 2 years and it seemed to work fine. I've never seen any parasitic flow through the FPHX when boiler wasn't running. The lines go "cold" until the next fire. Would it work better if the FPHX pickup and return were on their own line instead of load headers?
What bad juju do you say is happening in my headers?0 -
The way I'm looking at the diverter (or 3 way ZV) is if you were to pipe the garage loop through the run of a tee (instead of a bullhead where you have the diverter drawn in, turn a tee vertical so the tee is straight through to the garage and the branch of the tee looks to the storage tank) and put a 1 way ZV above this new tee to send all flow to storage while not in dump mode, through the branch of the tee. Water will take the path of least resistance during a dump when said ZV opens and head straight through the tee right? I had my wires crossed thinking about the diverter only being able to be fed from the bottom.
As for the headers, if you say they are working I guess that's that. My way of thinking is that incoming FPHX water is able to short cycle in the header and go right out to a load on a call for heat, which you say it does only during a burn? If it does it during a burn it's likely to do it during a no-fire draw as well, but seeing as you've run it this way and noticed no ghost flow perhaps there is enough hydraulic separation in the header to keep this ghost flow from happening. The bad juju mentioned is mostly just from a flow standpoint. Turbulence is a flow killer and counter flow in a pipe makes turbulence, similar to bullheading a tee, which is also a no-no. Notice almost any factory made buffer/storage tank has 4 ports, usually opposite each other, 2 for heat and 2 for load to keep things separated and allow full uninterrupted flow. If it works for you no sense in changing it because of what some clown on the internet said, but those are my thoughts anyway.
Side note though, how often are you burning and what is your heat load? 750 gallons would only make 312,375 BTU at a 50 degree delta T or 187,425 BTU at a 30 degree delta; 8k-13k BTU/H is pretty impressive for most homes with a garage if you burn once a day! Then again I'm using my Minnesota calculations where it may be 50 degrees colder than it is where you are lol0 -
The way it's plumbed now there is a short cycling effect in the headers while there is a fire burning. But while no fire is burning if there is any ghost flow through the lines to the FPHX it's so small the copper lines never get warm.
To answer the side note. I burn twice a day on the coldest days. Once in the morning before work and once at night before bed. During the more mild days I burn once a day at night. And shoulder days I burn every other day. I live in central Illinois so it winters probably aren't as crazy as yours.0 -
Warno, Those are some very nice welds on that pipe, looks like they were done with a TIG machine. The pipe looks like stainless and you have copper stubbed out of it. How did you do that?warno said:@Solid_Fuel_Man thanks for the reply. my thinking was the over heated water would circulate directly through the garage loop. If the dump is needed it's because the storage isn't taking any more heat from the boiler or at least not fast enough. The boiler is only plumbed to a FPHX which has the storage plumbed to the other side. So the storage tank gets heated before anything else.
@cutter thank you for the compliment. The welds were done with TIG. I've been doing it for about 13 years now. And yes it is stainless steel to copper transitions. The copper is simply sweat into the stainless with 50% silver solder. They are 1" sch40 stainless pipes bored out to fit the 1" copper inside. Then use a good acid based flux and 50% silver to make the sweat. It takes a quite abit of heat to get the stainless up to temp to take the solder. So it makes it alittle trickier then normal soft solder. I've attached a pic of stainless to copper and stainless to brass sweat joints I put together for this project.0
Warno, When I was In the Navy many years ago we used #1, #3 and #5 silver solder. I can't remember what each was used for. One of them was copper to copper or copper,nickel to brass another was used for copper to mild steel. I have some silver solder here I thought was 100% silver but I looked and it is 45% silver.warno said:@cutter thank you for the compliment. The welds were done with TIG. I've been doing it for about 13 years now. And yes it is stainless steel to copper transitions. The copper is simply sweat into the stainless with 50% silver solder. They are 1" sch40 stainless pipes bored out to fit the 1" copper inside. Then use a good acid based flux and 50% silver to make the sweat. It takes a quite abit of heat to get the stainless up to temp to take the solder. So it makes it alittle trickier then normal soft solder. I've attached a pic of stainless to copper and stainless to brass sweat joints I put together for this project.
My Tig skills are not as good as yours but I have a 1980 machine. I don't do that much Tig welding. The new machines make a world of difference in Tig welding. What you did not do was walk the cup around that pipe circumference. Just Kidding. Nice job0 -
Where i used to work we had 5%, 15%, and 50% silver. It was all Harris brand. We used the 5 and 15 for copper to copper and copper to brass. Then the 50% was for copper to stainless or copper to carbon. I don't have access to the high silver content filler anymore and to buy it is crazy money.
I'm running a Miller Dynasty 200 DX. I've had it since 2010 it's been a great machine. In the years I've been welding I still haven't mastered walking the cup. It seems the bigger the cup you're using the easier it is. And we never used the larger cups where I worked.0