I guess I could use a 2 pole contactor or a single zone valve relay. But the contactor is loud and an extra zone controller seems like overkill. I just need something to close an unpowered circuit (like an isolated end switch) when 24VAC is applied to the device.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,501
    RIB relay #RIBU1C, has a coil that will take 24v ac or dc or 120v ac. Has 1 set of single pole double throw contacts so you can use it with 1 nc contact or 1 no contact
    rick in Alaska
  • hot_rod
    hot_rod Member Posts: 23,412
    RIBs are quiet. or an induction relay on the 120 load
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • GW
    GW Member Posts: 4,832
    RIB !
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Parachute
    Parachute Member Posts: 25
    Thanks, all. Just ordered it.