Weil McLain Ultra II stuck on DHW
seandarcy
Member Posts: 21
in Gas Heating
This boiler serves for radiant and indirect DWH. The DWH aquastat is set for 120. The display on the boiler shows "4 180", all the time. I've tried Reset. I've tried powering it off and on. And, of course, this happens in the middle of a huge nor'easter !
Any help appreciated.
sean
Any help appreciated.
sean
0
Comments
-
Sequence 4 is DWH. You could temporarily disable DWH priority to get radiant up and running. It may be an issue with your dwh aquastat or wiring. Pics would be helpful. Here is control manual.0
-
I see you had issues with E02 and some aquastat issues. I would try disabling DWH parameter 2 by setting it to 0 and have a tech come out and hone in on the problem.0