ZC terminal
jackmc
Member Posts: 1
8124 aquastatt wired to R832a , ZC to 1 , ZR to 4 , 3 to circ , for 2 nd zone , Burham V83 with tankless coil , c1 drops out at correct temp 150 degrees from Low set at 160 , but ZC stays powered therefore 2 nd zone Circe keeps running when need heat for tankless , is this a bad 8124 ?
0
Comments
-
ZC should drop out on the low ...
There was an error rendering this rich post.
0 -
@jackmc
If C1 properly drops out (with the 'stat closed), and ZC remains powered, the only possibility is a bad L8124.1